Did the AHJ require that ever popular 10% cushion in the original calcs. Do
you make the curve without the 10% cushion if required?


On Sun, Sep 22, 2013 at 4:37 PM, Greg McGahan <[email protected]> wrote:

> We need to replace 3 painted heads in an existing storage room that
> currently has 14.5 k heads. Going to the closest Equivalent head changes
> the K factor to 14.0 and it makes enough of a difference that the calks no
> longer work……
>
> Even if we replace all of the heads in that area with 14.0's it will not
> work.  Does anyone happen to have these laying around?
>
> Question - if we can't find them, what should we do? The calcs do not work
> due to a combination of a slightly degraded water supply and being
> incorrectly calculated by the original installing contractor  - we have the
> original drawings and they used a .15 density throughout the building
> instead of the required .20. (yes- even when originally installed). The
> difference is only a few pounds, but it goes from slightly positive to
> negative. The AHJ has closed his ears and eyes and said "get the painted
> heads replaced".
>
> Thanks for your help.
> Greg
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to