Brian...the 1st 18" of spray pattern is golden...drop the pallet or move it
to one side at least 24" away from the deflector measured on the hypotenuse
from the closes edge of the pallet to the deflector....in the meantime...I
will try to figure out what architectural motif would a pallet hanging from
the ceiling fit into....

Steven Scandaliato, SET CFPS
520.971.2322 Cell

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian
Harris
Sent: Tuesday, September 24, 2013 7:51 AM
To: [email protected]
Subject: Sprinkler Obstruction

Quick question, A customer has a small retail store in their church and as
decoration has hung a wooded pallet horizontally from the ceiling. It's a
typical pallet with open space in between the slats, roughly 50% open area
and hangs about 12" below the sprinkler deflector, is a head required to be
added in the pallet?