Brian...the 1st 18" of spray pattern is golden...drop the pallet or move it to one side at least 24" away from the deflector measured on the hypotenuse from the closes edge of the pallet to the deflector....in the meantime...I will try to figure out what architectural motif would a pallet hanging from the ceiling fit into....
Steven Scandaliato, SET CFPS 520.971.2322 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris Sent: Tuesday, September 24, 2013 7:51 AM To: [email protected] Subject: Sprinkler Obstruction Quick question, A customer has a small retail store in their church and as decoration has hung a wooded pallet horizontally from the ceiling. It's a typical pallet with open space in between the slats, roughly 50% open area and hangs about 12" below the sprinkler deflector, is a head required to be added in the pallet? Brian Harris, CET BVS Systems Inc. Sprinkler Division bvssystemsinc.com<http://bvssystemsinc.com/> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org