Thanks Forest. We ended up presenting as you mentioned FM Datasheets as well as 
GAPs Guidelines and indicating the types of criteria that we would need to 
apply either one. I think they understood why it was impractical to state 
'provide sprinkler system in accordance with NFPA 30', when we have no 
knowledge of the classification of liquids/reactions that are being performed; 
and that it was beyond our role as a contractor. We have left it at their 
doorstep for them to review and come back with a specification, so we'll see 
what happens next.

Thanks again.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road, 
Cork, Ireland.
Office: (021) 496 5058
Mobile: (086) 788 8222
Fax: (021) 431 7425


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Forest 
Wilson Fire Sprinkler Comtractor
Sent: 24 October 2013 02:13
To: [email protected]
Subject: RE: Missing pages in NFPA 30

Ask if you can use FM standards?


Sent from my Galaxy S®III

-------- Original message --------
From: Damien Shannon <[email protected]>
Date: 10/23/2013  2:54 PM  (GMT-05:00)
To: [email protected]
Subject: RE: Missing pages in NFPA 30 
 
Hi Galen.

Thank you for the response.

The project in question is for a pharmaceutical manufacturing facility. The 
exact processing and liquids we don't know at the moment. We are meeting with 
the project Fire Safety Consultants tomorrow. However they don't seem to know 
too much about the sprinkler aspect (as we were told 'Sprinkler according NFPA 
30'). They have information on the liquids boiling points/flash... so they are 
knowledgeable in other aspects, so it is likely that they would be able to 
provide criteria, if we were able to say we need to know x,y,z in order to 
determine head spacing, fire area requirements, calc requirements.

The previous 'similar' projects that we have done have been per FM 7-32/7-14 
which would have that type of criteria that we could point to. However NFPA is 
referenced for this project.

Thanks again for any assistance.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road,
Cork, Ireland.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Taylor, 
Galen
Sent: 23 October 2013 19:27
To: [email protected]
Subject: RE: Missing pages in NFPA 30

Help us to help you - Define "processing" for us. For instance: Is it an oil 
refinery or a paint manufacturer.
Other terms for processing could be "use, mixing & dispensing". 

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Damien 
Shannon
Sent: Wednesday, October 23, 2013 6:50 AM
To: [email protected]
Subject: Missing pages in NFPA 30

So I'm not really missing pages, however some of the information I thought 
would be contained in chapter 17 doesn't seem to be in there. There seems to be 
extensive information related spacing, fire rating requirement and hydraulic 
calculation requirements for the various storage of liquids within NFPA 30, 
however there doesn't seem to be such criteria for Processing Facilities.

Can anyone advise where one goes for criteria for an internal processing 
facility utilizing flammable and combustible liquids (both miscible and
immiscible) in regards to:
Max allowable spacing of sprinklers?
Do you have to flow all sprinklers within a fire area (i.e. including 
sprinklers under platforms, under obstructions, over the liquid pumps)?
What is the required calculation area and density? I see 3.3.2.2 defines a Fire 
Area as 'An area of a building separated from the remainder of the building by 
construction having a fire resistance of at least one hour and having all 
communicating opening properly protected by an assembly having a fire 
resistance rating of at least one hour. However, if you have a large area and 
trench drains are provided to prevent spill fires, what is the maximum area to 
calculate?

First NFPA job in 3 years and it would be one that I'm familiar not with.

Any insight would be greatly appreciated. 

Regards.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road,
Cork, Ireland.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to