Damien,

You said,


"Thanks Forest. We ended up presenting as you mentioned FM Datasheets as 
well as GAPs Guidelines and indicating the types of criteria that we 
would need to apply either one. I think they understood why it was 
impractical to state 'provide sprinkler system in accordance with NFPA 
30', when we have no knowledge of the classification of 
liquids/reactions that are being performed; and that it was beyond our 
role as a contractor. We have left it at their doorstep for them to 
review and come back with a specification, so we'll see what happens 
next."


This is the correct approach.  It is the design Engineer of Record's 
responsibility to determine the protection requirements.

You cannot just pick up NFPA 30 and go the Chapter 17 and find all of the 
requirements for protection of flammable & combustible liquids processes.  You 
have to use all of the applicable requirements in the documents, and you need 
to use professionals who are familiar with the processes and the hazards 
associated with those processes.  Take a look at all the requirements in 
general provisions in Chapter 6, not just 6.7 which covers fire protection and 
fire suppression.  If one don't understand the hazard (section 6.4) it is less 
likely that the protection provided, whatever is decided, will be adequate.  If 
you find information in the FM Data Sheets that is specific to what you are 
trying to protect, then it is appropriate for the design professionals to 
consider that as the means of protection.  If it doesn't quite fit, then it 
requires that the people designing the system evaluate if it is appropriate for 
the hazard and determine whether or not to
 specify it as appropriate.

One of the reasons that the protection criteria for process protection is not 
as specific as the protection criteria for storage of flammable & combustible 
liquids is the wide variation of how things are used in process operations, and 
the breadth of coverage from household use to large industrial processing 
facilities.  The protection criteria for storage is based on large scale 
testing.  With few exceptions it is based on tests that have been proven to 
work on that specific configuration of container(s), materials,and storage 
configuration.  If it hasn't been tested, you won't find criteria in the 
standard.  Even less testing has been done with process operations, which is 
why the hazard analysis is important and to be performed by experienced 
professionals.  Most process protection has been developed by the industries 
and their insurance companies over time in an effort to minimize loss.

As always, the opinions expressed are my own and are not to be taken as an 
interpretation, informal or otherwise, of the NFPA or any of my affiliations.

Dwight Havens
Pre-Planning Engineer, Round Lake Fire Department, Round Lake, NY

Chairman, NFPA 30 FLC-OPS




On Friday, October 25, 2013 5:44 AM, Damien Shannon <[email protected]> wrote:
 
Thanks Forest. We ended up presenting as you mentioned FM Datasheets as well as 
GAPs Guidelines and indicating the types of criteria that we would need to 
apply either one. I think they understood why it was impractical to state 
'provide sprinkler system in accordance with NFPA 30', when we have no 
knowledge of the classification of liquids/reactions that are being performed; 
and that it was beyond our role as a contractor. We have left it at their 
doorstep for them to review and come back with a specification, so we'll see 
what happens next.

Thanks again.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road, 
Cork, Ireland.
Office: (021) 496 5058
Mobile: (086) 788 8222
Fax: (021) 431 7425


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Forest 
Wilson Fire Sprinkler Comtractor
Sent: 24 October 2013 02:13
To: [email protected]
Subject: RE: Missing pages in NFPA 30

Ask if you can use FM standards?


Sent from my Galaxy S®III

-------- Original message --------
From: Damien Shannon <[email protected]>
Date: 10/23/2013  2:54 PM  (GMT-05:00)
To: [email protected]
Subject: RE: Missing pages in NFPA 30 

Hi Galen.

Thank you for the response.

The project in question is for a pharmaceutical manufacturing facility. The 
exact processing and liquids we don't know at the moment. We are meeting with 
the project Fire Safety Consultants tomorrow. However they don't seem to know 
too much about the sprinkler aspect (as we were told 'Sprinkler according NFPA 
30'). They have information on the liquids boiling points/flash... so they are 
knowledgeable in other aspects, so it is likely that they would be able to 
provide criteria, if we were able to say we need to know x,y,z in order to 
determine head spacing, fire area requirements, calc requirements.

The previous 'similar' projects that we have done have been per FM 7-32/7-14 
which would have that type of criteria that we could point to. However NFPA is 
referenced for this project.

Thanks again for any assistance.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road,
Cork, Ireland.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Taylor, 
Galen
Sent: 23 October 2013 19:27
To: [email protected]
Subject: RE: Missing pages in NFPA 30

Help us to help you - Define "processing" for us. For instance: Is it an oil 
refinery or a paint manufacturer.
Other terms for processing could be "use, mixing & dispensing". 

Galen Taylor
County of Los Angeles Fire Department
Fire Prevention Engineering
323-890-4339
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Damien 
Shannon
Sent: Wednesday, October 23, 2013 6:50 AM
To: [email protected]
Subject: Missing pages in NFPA 30

So I'm not really missing pages, however some of the information I thought 
would be contained in chapter 17 doesn't seem to be in there. There seems to be 
extensive information related spacing, fire rating requirement and hydraulic 
calculation requirements for the various storage of liquids within NFPA 30, 
however there doesn't seem to be such criteria for Processing Facilities.

Can anyone advise where one goes for criteria for an internal processing 
facility utilizing flammable and combustible liquids (both miscible and
immiscible) in regards to:
Max allowable spacing of sprinklers?
Do you have to flow all sprinklers within a fire area (i.e. including 
sprinklers under platforms, under obstructions, over the liquid pumps)?
What is the required calculation area and density? I see 3.3.2.2 defines a Fire 
Area as 'An area of a building separated from the remainder of the building by 
construction having a fire resistance of at least one hour and having all 
communicating opening properly protected by an assembly having a fire 
resistance rating of at least one hour. However, if you have a large area and 
trench drains are provided to prevent spill fires, what is the maximum area to 
calculate?

First NFPA job in 3 years and it would be one that I'm familiar not with.

Any insight would be greatly appreciated. 

Regards.

Damien Shannon
Provincial Sprinkler Company Ltd.
Unit 4, Cork Airport Industrial Estate
Kinsale Road,
Cork, Ireland.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to