Jay: That is a provision from 13D and not applicable to 13R.
Mike Cabral Cell 314-412-1800 On Thursday, November 14, 2013 5:07 PM, Jay Stough <[email protected]> wrote: We are taking over the project on a 6 family dwelling unit. Since I don't do residential often, I want to make sure I am reading things correctly. The contractor that installed the previous buildings has the sprinklers in the basement at the same level as the duct running down the middle, I guess counting on the fact that the ceiling will likely be finished at some point. Without a finished ceiling, I can't find anything in 13R that allows you to do this. Am I correct or am I missing something? Jay Stough Tilley Fire Equipment Doylestown, PA _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org