Jay: That is a provision from 13D and not applicable to 13R.

 
Mike Cabral
Cell 314-412-1800





On Thursday, November 14, 2013 5:07 PM, Jay Stough <[email protected]> wrote:
 
We are taking over the project on a 6 family dwelling unit.  Since I don't do 
residential often, I want to make sure I am reading things correctly.  The 
contractor that installed the previous buildings has the sprinklers in the 
basement at the same level as the duct running down the middle, I guess 
counting on the fact that the ceiling will likely be finished at some point.  
Without a finished ceiling, I can't find anything in 13R that allows you to do 
this.  Am I correct or am I missing something?


 
Jay Stough
Tilley Fire Equipment
Doylestown, PA