Duane, 7.9.1 is simply saying ignore the section when dealing with refrigerated spaces above freezing temps. Is doe NOT say ignore other sections such as 8.16.2.3.3. I.e. follow the standard, but skip over 7.9. So pitch the main at 1/2" in 10' (or greater).
Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | http://www.kfiengineers.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Martinez, Dewayne Sent: Thursday, December 05, 2013 12:40 PM To: [email protected] Subject: Dry system main pitch in cooler NFPA 13 (07ed) What pitch does a dry system main have to be in a refrigerated space (>32F)? 8.16.2.3.3 states ½ in 10 but when you look at 7.9.1 it say's to ignore the requirements of 7.9 (Refrigerated Spaces)when the temperature is greater than 32F. Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org