What is confusing to me is that 7.9 refers you to 8.16.2.3.3.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark A. 
Sornsin, P.E.
Sent: Thursday, December 05, 2013 12:46 PM
To: [email protected]
Subject: RE: Dry system main pitch in cooler

Duane,

7.9.1 is simply saying ignore the section when dealing with refrigerated spaces 
above freezing temps.  Is doe NOT say ignore other sections such as 8.16.2.3.3. 
 I.e. follow the standard, but skip over 7.9. So pitch the main at 1/2" in 10' 
(or greater).

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Martinez, 
Dewayne
Sent: Thursday, December 05, 2013 12:40 PM
To: [email protected]
Subject: Dry system main pitch in cooler

NFPA 13 (07ed)

What pitch does a dry system main have to be in a refrigerated space (>32F)?  
8.16.2.3.3 states ½ in 10 but when you look at 7.9.1 it say's to ignore the 
requirements of 7.9 (Refrigerated Spaces)when the temperature is greater than 
32F.

Thanks,

Dewayne



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to