The original reference by Ron F. below is from NFPA 13-2010.

I am now wondering if the response by Roland would indeed apply
"...throughout buildings". Specifically, can we use intermediate temp
residential heads in a dorm room even if far enough away from a heat source
to use ordinary temp? 8.3.2.5* (8) makes me wonder, even though it is lumped
with other than residential areas (or maybe because it is!).

thanks,
Brad

-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Monday, October 14, 2013 10:48 AM
To: [email protected]
Subject: RE: Ordinary vs intermediate temperature heads

Thanks for the reply. There were some doubters here that wanted to see
confirmation from another source.

Ron F

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Monday, October 14, 2013 8:31 AM
To: [email protected]
Subject: Re: Ordinary vs intermediate temperature heads

That is indeed what it means.  We submitted the proposal on this issue a
couple of cycles ago and the justification states it in just that fashion.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org

On Oct 14, 2013, at 8:12 AM, <[email protected]> wrote:

> 8.3.2.1*   Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or
8.3.2.5 are met, ordinary- and intermediate-temperature sprinklers shall be
used throughout buildings.
> 
> Does this mean that we can use intermediate temp QR's throughout a LH
occupancy? This would eliminate the need to figure out where intermediates
are needed because of heat sources.
> 
> Ron F
> 