NFPA 13, 2013 edition
8.17.4.1.1 Main drain test connections shall be provided at
locations that will permit flow tests of water supplies and
connections.

NFPA 25, 2014 edition
13.2.5* Main Drain Test. A main drain test shall be conducted
annually for each water supply lead-in to a building water based
fire protection system to determine whether there has
been a change in the condition of the water supply.

A.13.2.5 Main drains are installed on system risers for one
principal reason: to drain water from the overhead piping after
the system is shut off. This allows the contractor or plant
maintenance department to perform work on the system or to
replace nozzles after a fire or other incident involving system
operation.
Data collected from the suction gauges during a fire pump
flow test that test the water supply would satisfy the requirements
for a main drain test.

13.2.5.1 Where the lead-in to a building supplies a header or
manifold serving multiple systems, a single main drain test
shall be permitted.

13.2.5.2 In systems where the sole water supply is through a
backflow preventer and/or pressure-reducing valves, the main
drain test of at least one system downstream of the device shall
be conducted on a quarterly basis.


Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"

-----Original Message-----
From: Tom Duross [mailto:[email protected]] 
Sent: Friday, December 13, 2013 5:22 AM
To: [email protected]
Subject: RE: Fire Pump Room Main Drain

Thanks but I respectfully kinda disagree.
If I start by testing the pump (0-150%), then move to test each floor, check 
TS, open ITV and time zone and main WFS; I'm not done.  The more I write this 
the more I think how silly a main drain test is with a pump but there's no 
minimum requirement excepting me from a main drain test when I have a pump and 
the sprinkler standard actually states it should be on the street side of the 
pump.  I can almost hear the phone ringing from George, he'd have been up for 
an hour at this time of the morning and skipping the keyboard for a good 
morning call, coffee in one hand and a butt in the other.  I'm going to suggest 
to the client he invest in a new main drain (and riser gauge) on the city side 
and replace the leaking main drain (which is really just a drain imho) on the 
system side and we test and tag city side valve.  For what I don't know, seems 
a waste of time and water.  BTW, their pump is done over, 39 year old Patterson 
that sounded like a bucket of bolts and now the loudest 
 sound coming from it is the 55L dumping down the drain.  Totally rebuilt, even 
grouted and painted.


Tommy (Yo, dude!),
The Pump IS the water supply.  In order to drain the system, the Main Drain 
needs to be on the system side of the pump.  And in order to test the water
supply to the system (ie: city water + pump.   dammit), you gotta flow the
water from the city supply through the pump and to the system.  This is even 
more critical when you are supplying multiple standpipes AND sprinklers.  
NFPA 25 requires an analysis of the city water supply at 5 years.  
Tom, the beauty of what you do is that you ALWAYS think about the best interest 
of the owner.  And you should rock on in giving the owner the cadillac!  But 
that is not what the NFPA standards are all about (even if we want to encourage 
such a thing).  NFPA has to draw a line at what the minimum acceptable safety 
standard should be.  
The minimum (and it is quite acceptable) is to install a drain (call it 
main...and each floor would end up having one, right?) and use it to determine 
whether the ENTIRE water supply is adequate.  There ya go.

It should be recognized that the above is my opinion as a member of the NFPA, 
(you know... 3,4,13,14,25,72,88A & stuff) and has not been processed as a 
formal interpretation in accordance with the NFPA Regulations Governing 
Committee Projects and should therefore not be considered, nor relied upon, as 
the official position of the the NFPA, nor any of their technical committees. 

Sincerely,


Cecil Bilbo 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to