Tom,
leave it whre it is at for drain porposes. Youe mentioned that the pump has
a bypass. Turn the pump off for the main drain test and test through the
bypass.
Glen buelow


On Thu, Dec 12, 2013 at 4:55 PM, Charles Thurston <[email protected]>wrote:

> "Hello All,
>
> Would not the test point to test the forward flow of the backflow
> preventer at system demand do the same thing as the main drain before the
> pump?
>
> Thursday, December 12, 2013, 4:07:24 PM, you wrote:
>
> > You would want a main drain where it is installed so the system can
> > be drained for maintenance, hence the word drain. Do you need
> > another drain on the suction side of a pump for a test to verify
> > condition? There is some merit to that idea.
>
> > Todd G Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > www.fpdc.com
> > 860-535-2080 (ofc)
>
> >> On Dec 12, 2013, at 3:49 PM, "Tom Duross" <[email protected]> wrote:
>
> >> I'm looking for opinions on this.
>
> >> A new building I just took over ITM on has a fire pump feeding
> combination
> >> standpipes, fully sprinklered high-rise circa 1974.
> >> Existing 2" main drain is toast, handle broken, stem all chewed up from
> >> wrenching.
> >> I proposed we change it, use a 300# ball valve, galvy pipe; do it right.
> >> BUT, it's on the system riser off the pump discharge and I say wrong
> >> location.
> >> Even the standard still says do a main drain test when you have a fire
> pump
> >> (imho silly), so I do.
> >> A main drain test is to verify supply condition.  I say with it where
> it is,
> >> we either have to drop the building to street pressure OR do a main
> drain
> >> with the pump running.  In a case like this I always do the latter but
> I see
> >> others dropping the building and I think it's unnecessary and an
> impairment.
> >> The problem I have with doing 150-200# main drain tests is they do dump
> a
> >> ton of water, even with a fire hose off the 2" el and a hose monster.
> >> I feel it's overkill and unnecessary on top of a waste of time but
> whatever.
> >> My issue (finally) is where to properly place a main drain when you
> have a
> >> pump.  I say on the street side bypass supply, just flow supply
> pressure and
> >> be done with it.  Facilities guy says others dumped building and just do
> >> that.
> >> Sprinklers are tested with the pump running, last few companies shut it
> off
> >> and went on jockey, that's why they're gone.
> >> Looking for opinions and even second opinions (ok you're ugly too).
> >> What's the proper location?
>
> >> TD
>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> --
> Best regards,
>  Charles                            mailto:[email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
*Glen Buelow*



*Glen W. Buelow, Inc.Fire Protection Design and ConsultingCleveland
330.220.7201 *●* Akron 330.665.4439*
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to