Chris,

Did you ask the contractor about the elevations of the hydrants?

The only way I see the gaged and flowed PSI both 20 is if the flowed is
about 8 feet lower than the gaged and the margin of error in synchronization
of the gages is a pound or 2.

I got the 7'-11" elevation difference using my secret recipe of definite
proportions of feet and seconds with a dash of pure gravity on top ;)  

thanks, Brad

-----Original Message-----
From: Cahill, Christopher [mailto:[email protected]] 
Sent: Thursday, December 19, 2013 11:30 AM
To: [email protected]
Subject: RE: Flow Test Residual and Pitot The Same?

Well done Mark - Exactly.  And what I'm hearing thus far is yes it's
possible. If I were standing there I wouldn't ask the question.  I'd see
what was going on and trust the results. When I'm not there, and no one I
trust, I get skeptical.  

I guess the good news is the test is such crap they will have a pump.  If
it's a bad test and they really have more water no harm except to the owners
pocket book.  If it were showing we didn't need a pump but was really less
than reported that would potentially make the sprinklers ineffective.  I
realize even with the pump in this case the test could be worse and still
short on water.  But as bad as it is, odds are it can't be much worse.  Much
more harm if there is a fire and short on water.   

The report is issued correct, the contractor described a correct process so
I guess I have to reluctantly accept.  About the only unknown is calibration
of the gauges.  I suppose I can ask and will get a certificate showing they
are.  But just like the flow report and description of the procedure it's
all trusting the other end is honest. 

I just found painted heads in a building where they haven't started painting
anything....hmm, trying to reuse heads?  I know most folks are honest but a
few mistakes do occur.  

Chris Cahill, PE*
Senior Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Mark A.
Sornsin, P.E.
Sent: Thursday, December 19, 2013 10:33 AM
To: [email protected]
Subject: RE: Flow Test Residual and Pitot The Same?

Tim - If I may speak for Chris - he is not confusing the residual with the
Pitot. He's simply noting that a contractor has told him their test shows a
Pitot pressure that is the same value as the Residual pressure. So the
question is  "Is this possible?"

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of G. Tim
Stone
Sent: Thursday, December 19, 2013 5:58 AM
To: [email protected]
Subject: RE: Flow Test Residual and Pitot The Same?

Chris,
My understanding is that you are asking about 2 different pressures. The
Static and Residual pressure readings we acquire are acting in all
directions inside a pressurized pipe. Static or dynamic represents pressure
of at rest or non moving/flowing condition while the residual lower change
in pressure we expect to see when water is allowed to flow from an open
valve.

>From the next hydrant that is allowed to flow we are measuring for GPM by
use of the Pitot which is measuring the pressure at the center of that water
flow stream and that pressure is created by the force of that moving water
past the end of the Pitot.

These are two different pressures and should not be confused.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Cahill, Christopher
> Sent: Wednesday, December 18, 2013 5:44 PM
> To: [email protected]
> Subject: Flow Test Residual and Pitot The Same?
>
> I have a flow test report showing the residual and pitot pressure 
> being
the
> same.  60 static, 20 residual with a 20 pitot on a 2.5" opening for
> 750 gpm. I talked to the contractor and they described doing it 
> correctly, two hydrants one static/residual, one flowing.  I don't 
> believe it's possible to have the residual and pitot the same pressure 
> but I'm having a hard
time
> articulating why not.  I know I've never seen this before and probably
have
> done almost 1,000 tests in my life.  Any input?  Is it possible?
> Either way why or why not?
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For 
> *Registered
in:
> MN
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
> firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to