I have a question:

A few weeks ago, I posted that I had conducted a main drain test on a system installed in 1996.
Since installation, this was the first main drain test performed.
The Hydraulic Calc Plaque showed residual 40 psi.
My main drain test was 15 psi.

Since the difference exceeded 10%, and there were no former main tests to compare to, I compared to the Hydraulic plaque and wrote the owner a letter informing them that the system may be impaired and recommended further investigation. I recommended that they obtain the Contractors Test Certificate since that is the only main drain we can compare to.

The owner has been unable to obtain the Test Cert.
They contacted the installation contractor and the contractor has the As-Builts and original hydrant flow test but not the Test Certificate. As a side note, the installation was terrible, upright sprinklers installed 6' below roof level, upright installed as a pendent, etc. I didnt note these on the inspection since I was just doing an NFPA 25 inspection.

What is the recommended course of action?
I don't need suggestions about NFPA 25 or liability to me (the owner is an organization I belong to)
; What is the recommended course of action for the owner?

--
Forest Wilson
Project Manager

1855 Bellbrook Ave Ste C
Xenia OH 45385
Ph: 937-736-0425

///WHO IS JOHN GALT?///

******This email and any files transmitted with it are confidential and 
intended solely for the use of the individual or entity to whom they are 
addressed. If you have received this email in error please notify the system 
manager. This message contains confidential information and is intended only 
for the individual named. If you are not the named addressee you should not 
disseminate, distribute or copy this e-mail. Please notify the sender 
immediately by e-mail if you have received this e-mail by mistake and delete 
this e-mail from your system. If you are not the intended recipient you are 
notified that disclosing, copying, distributing or taking any action in 
reliance on the contents of this information is strictly prohibited.***

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to