In this particular case (and is often the case) the wall is not a rated
assembly.  But that's OK, because 11.2.3.3.3 doesn't require it to be a
rated assembly, just to have a 30 minute fire-resistance rating (light
hazard).  This wall has 5/8" type X gyp on both sides.  Per the National
Gypsum website, 2 layers of 5/8 type X (1 on each side) give a
fire-resistance rating of 1 hour.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Thursday, January 16, 2014 3:45 PM
To: [email protected]
Subject: RE: Glass & room design

It says, " ... rooms shall be enclosed with walls having a fire
resistance rating equal to the water supply duration ..."    If the wall
is a rated assembly and the glazing is within the allowable gross area for
unprotected openings, then I would assume that you can do it.
Consult the building code for the allowable openings, glazed area, protected
and unprotected, etc., etc.

Steve L.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed
Kramer
Sent: Thursday, January 16, 2014 1:42 PM
To: [email protected]
Subject: Glass & room design

Reference NFPA 13 ('13) section 11.2.3.3.3.  "To utilize the room design
method, all rooms shall be enclosed with walls having a fire-resistance
rating equal to the water supply duration indicated in Table 11.2.3.1.2."  

 

In light hazards, self-closing doors are exempt (they are allowed to be
non-rated).  What about a non-operable window in the wall between an office
and a corridor - is it required to be 30 minute rated?

Let's say the window is 6' wide x 4' tall with an 8" deep (or deeper) lintel
above it.  When calculating the office using the room design method, am I
required to include 2 spirnks on the other side of the window?

 

What if the window was full-height (no lintel above it), does that change
anything?

 

What if we change the window to a full-height glass wall?  I'm trying to
wrap my head around the role glass plays (or doesn't play) in applying the
room design method.

 

Ed Kramer

Lawrence, KS

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to