the number of layers is for a single membrane (aka one side of the studs).  

Although logic could lead one to say having an non-rated door is no different 
than a non-rated window,  13 specific allows the door.  There's a significant 
difference, though, between glass and wood and how they react to fire (and 
thermal shock when the sprinkler goes off).  11.2.3.3.5(2) explicits tells us 
how to address unprotected openings. Full steam ahead.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jan 16, 2014, at 2:01 PM, Ed Kramer <[email protected]> wrote:

> In this particular case (and is often the case) the wall is not a rated
> assembly.  But that's OK, because 11.2.3.3.3 doesn't require it to be a
> rated assembly, just to have a 30 minute fire-resistance rating (light
> hazard).  This wall has 5/8" type X gyp on both sides.  Per the National
> Gypsum website, 2 layers of 5/8 type X (1 on each side) give a
> fire-resistance rating of 1 hour.