here's the text that mad win into the First Draft

New section 6.4.8. Extension fittings.
6.4.8.1: the outlet diameter of the extension fittings shall be equal to the 
inlet diameter of the sprinkler.
6.4.8.2: a single extension fitting up to a maximum of 2 inches in length shall 
be permitted to be installed with a sprinkler.
6.4.8.2.1: the extension fitting shall be included in the hydraulic 
calculations.
6.4.8.2.2: the requirement of 6.4.8.2.1 shall not apply where the sprinkler is 
listed for use with the extension nipple.




Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Jan 20, 2014, at 1:39 PM, Roland Huggins <[email protected]> wrote:

> You hit it on the nose when indicating that the 1" restriction is on PIPE.  
> Does this limit apply to fittings?  Well the real question since we know 1/2" 
> outlets are ok is not the standard fitting but nipple extensions.  That's an 
> issue that the standard has not yet addressed.  There have been cases where 2 
> or 3 extensions have been combined (and probably not included in the 
> calculations).  I believe something on it will be in the next addition.
> 
> Roland
> 
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
> On Jan 17, 2014, at 3:19 PM, Forest Wilson Fire Sprinkler Contractor 
> <[email protected]> wrote:
> 
>> I dont underatand how a fitting would be considered a pipe nipple. 
>> The prohibition against using 1/2" pipe in earthquake zones should not apply 
>> to the use of street l fittings. 
>> 
>> If it did, then the same argument could could made against using any 1/2" 
>> fitting.  
>> 
>> 
>> Forest Wilson
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org