Ron,
I saw Mr. Scandaliato's name on that Ceiling Cloud Study and I have seen him 
distinguish between Storage and everything less so I think he knows things we 
don't yet so that's why I said the 'put it in a nutshell' part

> On Feb 8, 2014, at 4:21 PM, Brad Casterline <[email protected]> wrote:
> 
> I'm thinking the ceiling jet of storage fires are more complicated under 
> sloping roofs than just saying we will be fine if we figure the highest point 
> and call everywhere else flat equal to that height.
> 
>> On Feb 8, 2014, at 3:29 PM, "rongreenman ." <[email protected]> wrote:
>> 
>> Well, the IBC says 1:12, 5%, and under to be flat. The Europeans seem to
>> use 7%, 1.47:12. The AIA has multiple answers. One faction of the roofing
>> guys say 1:12, and another says 2:12. They call 2:12 steep slope flat, and
>> less low slope flat. So there you have it, after at least seven minutes of
>> research.
>> 
>> 
>> On Sat, Feb 8, 2014 at 10:49 AM, Brad Casterline 
>> <[email protected]>wrote:
>> 
>>> I'll get you a case* and all the time you need if you can put it in a
>>> nutshell-- the suspense is killing me! Were there any darts involved?
>>> 
>>> *quantity=30, not 24, according to my son's fraternity I TAPPA KEG
>>> 
>>> :)
>>> 
>>> -----Original Message-----
>>> From: Steven Scandaliato [mailto:[email protected]]
>>> Sent: Wednesday, February 05, 2014 3:41 PM
>>> To: [email protected]
>>> Subject: RE: Ceiling Slope Limit for Storage
>>> 
>>> ...  The good question to ask now is where did we get the 2/12 pitch as the
>>> line for flat versus slope?  Someone get me a beer and a few hours...
>>> 
>>> Steven Scandaliato, SET CFPS
>>> Principal
>>> 520.971.2322
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> 
>> -- 
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis Bacon,
>> essayist, philosopher, and statesman (1561-1626)
>> 
>> A problem well stated is a problem half solved. -Charles F. Kettering,
>> inventor and engineer (1876-1958)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to