I just read in my 16th edition FP Handbook that the ideal top of storage to 
sprinkler clearance is between 1.5 and 4.5 feet. To fall within this 3 foot 
range under a 2 in 12 slope the horizontal 'footprint' of the storage area 
would be 18 feet. A double row rack with an 18" flue plus 4 feet to the center 
of the aisle on both sides would be close to that???

> On Feb 8, 2014, at 5:07 PM, Brad Casterline <[email protected]> wrote:
> 
> Ron,
> I saw Mr. Scandaliato's name on that Ceiling Cloud Study and I have seen him 
> distinguish between Storage and everything less so I think he knows things we 
> don't yet so that's why I said the 'put it in a nutshell' part
> 
>> On Feb 8, 2014, at 4:21 PM, Brad Casterline <[email protected]> wrote:
>> 
>> I'm thinking the ceiling jet of storage fires are more complicated under 
>> sloping roofs than just saying we will be fine if we figure the highest 
>> point and call everywhere else flat equal to that height.
>> 
>>> On Feb 8, 2014, at 3:29 PM, "rongreenman ." <[email protected]> wrote:
>>> 
>>> Well, the IBC says 1:12, 5%, and under to be flat. The Europeans seem to
>>> use 7%, 1.47:12. The AIA has multiple answers. One faction of the roofing
>>> guys say 1:12, and another says 2:12. They call 2:12 steep slope flat, and
>>> less low slope flat. So there you have it, after at least seven minutes of
>>> research.
>>> 
>>> 
>>> On Sat, Feb 8, 2014 at 10:49 AM, Brad Casterline 
>>> <[email protected]>wrote:
>>> 
>>>> I'll get you a case* and all the time you need if you can put it in a
>>>> nutshell-- the suspense is killing me! Were there any darts involved?
>>>> 
>>>> *quantity=30, not 24, according to my son's fraternity I TAPPA KEG
>>>> 
>>>> :)
>>>> 
>>>> -----Original Message-----
>>>> From: Steven Scandaliato [mailto:[email protected]]
>>>> Sent: Wednesday, February 05, 2014 3:41 PM
>>>> To: [email protected]
>>>> Subject: RE: Ceiling Slope Limit for Storage
>>>> 
>>>> ...  The good question to ask now is where did we get the 2/12 pitch as the
>>>> line for flat versus slope?  Someone get me a beer and a few hours...
>>>> 
>>>> Steven Scandaliato, SET CFPS
>>>> Principal
>>>> 520.971.2322
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> 
>>> 
>>> -- 
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> [email protected]
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis Bacon,
>>> essayist, philosopher, and statesman (1561-1626)
>>> 
>>> A problem well stated is a problem half solved. -Charles F. Kettering,
>>> inventor and engineer (1876-1958)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to