I just read in my 16th edition FP Handbook that the ideal top of storage to sprinkler clearance is between 1.5 and 4.5 feet. To fall within this 3 foot range under a 2 in 12 slope the horizontal 'footprint' of the storage area would be 18 feet. A double row rack with an 18" flue plus 4 feet to the center of the aisle on both sides would be close to that???
> On Feb 8, 2014, at 5:07 PM, Brad Casterline <[email protected]> wrote: > > Ron, > I saw Mr. Scandaliato's name on that Ceiling Cloud Study and I have seen him > distinguish between Storage and everything less so I think he knows things we > don't yet so that's why I said the 'put it in a nutshell' part > >> On Feb 8, 2014, at 4:21 PM, Brad Casterline <[email protected]> wrote: >> >> I'm thinking the ceiling jet of storage fires are more complicated under >> sloping roofs than just saying we will be fine if we figure the highest >> point and call everywhere else flat equal to that height. >> >>> On Feb 8, 2014, at 3:29 PM, "rongreenman ." <[email protected]> wrote: >>> >>> Well, the IBC says 1:12, 5%, and under to be flat. The Europeans seem to >>> use 7%, 1.47:12. The AIA has multiple answers. One faction of the roofing >>> guys say 1:12, and another says 2:12. They call 2:12 steep slope flat, and >>> less low slope flat. So there you have it, after at least seven minutes of >>> research. >>> >>> >>> On Sat, Feb 8, 2014 at 10:49 AM, Brad Casterline >>> <[email protected]>wrote: >>> >>>> I'll get you a case* and all the time you need if you can put it in a >>>> nutshell-- the suspense is killing me! Were there any darts involved? >>>> >>>> *quantity=30, not 24, according to my son's fraternity I TAPPA KEG >>>> >>>> :) >>>> >>>> -----Original Message----- >>>> From: Steven Scandaliato [mailto:[email protected]] >>>> Sent: Wednesday, February 05, 2014 3:41 PM >>>> To: [email protected] >>>> Subject: RE: Ceiling Slope Limit for Storage >>>> >>>> ... The good question to ask now is where did we get the 2/12 pitch as the >>>> line for flat versus slope? Someone get me a beer and a few hours... >>>> >>>> Steven Scandaliato, SET CFPS >>>> Principal >>>> 520.971.2322 >>>> >>>> _______________________________________________ >>>> Sprinklerforum mailing list >>>> [email protected] >>>> >>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>> >>> >>> >>> -- >>> Ron Greenman >>> Instructor >>> Fire Protection Engineering Technology >>> Bates Technical College >>> 1101 So. Yakima Ave. >>> Tacoma, WA 98405 >>> >>> [email protected] >>> >>> http://www.bates.ctc.edu/fireprotection/ >>> >>> 253.680.7346 >>> 253.576.9700 (cell) >>> >>> Member: >>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC >>> >>> They are happy men whose natures sort with their vocations. -Francis Bacon, >>> essayist, philosopher, and statesman (1561-1626) >>> >>> A problem well stated is a problem half solved. -Charles F. Kettering, >>> inventor and engineer (1876-1958) >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org