Yes. Many standard spray sprinklers are listed for 250. However, to my 
knowledge, UL test for strength and not spray pattern/droplet performance. 

Thanks,
John August Denhardt P.E.

> On Feb 18, 2014, at 6:01 PM, "Roland Huggins" <[email protected]> 
> wrote:
> 
> initially the higher pressure listing on sprinklers was just for Light Hazard 
> occupancies.  I have not looked lately.  Have they been expanded to OH?
> 
> Roland
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
> 
> 
> 
> 
> 
>> On Feb 18, 2014, at 2:43 PM, Jim Davidson <[email protected]> 
>> wrote:
>> 
>> To all design the sprinkler system with 250 psi rated sprinkler heads and 
>> 300 psi pipe and fittings.
> 