It does stink to have to install a prv for a single floor but the code is
the code.  
It happens all the time in high rises when you hit the 175 break.
Double check the JP settings, JP off should be right on churn (technically
maximum expected churn) or 3-5 PSI above for fluctuating street supplies.

TD

 Ron,

1. The engr firm is correct...anything over 175-psi requires a PRV and the
maximum expected static pressure (churn pressure) is used to determine where
the PRV's are required.

2. If you do not put the PRV and something starts to leak and cause water
damage, then you will assume responsibility.

3. I agree with you 100%...that the churn pressure only exists during the
pump tests and that a city water supply may vary as much as 10 to 15-psi
during the day so most of the time it will actually be less than 175-psi. 

4. I also feel that installing a PRV for the "excessive" 3-psi is a waste of
time and money. The hydrant test was done with a gauge that was bouncing
around between 4 to 6-psi, and what if it was only 176-psi instead of
178-psi. However, I am not the responsible party to address this issue from
a liability perspective.
rick