I have to agree with Ron.  For years I have installed EQ braces using quick 
straps and 1" braces.  Always was under the impression that these were spaced 
in accordance with NFPA13.  It wasn't until I was required through a plan 
review years later ( then as a designer ) to calculate the bracing that I 
grasped the depth of consideration and planning involved with determining what 
kind, how closely spaced, what size, ..... . Not to mention what you gain or 
loose based on spacing,  how the ZOI can be effected by going the 40' max 
instead of say 30'.

Granted, today as an owner I only deal with the occasional category C and our 
plan reviews are typically by some EIT looking at a checklist he/she has on the 
screen in front of them requesting seismic calculations,  .... having no idea 
how to read them.   Still, if we are going to take the authority to require 
them and the time to install them, ... We should at least do them right.


My two cents. 


Sent from my Verizon Wireless 4G LTE smartphone

-------- Original message --------
From: "rongreenman ." <[email protected]> 
Date:02/20/2014  10:12 PM  (GMT-07:00) 
To: [email protected] 
Subject: Re: seismic bracing calcs 

How do you locate per 13? How do you know what you did will work? How do
you know that 1" x 34" brace at 37 degrees to side of a beam doesn't need
to be shorter, at a different angle, or a 1 1/4" brace, without doing
calcs? 13 only tells you the general and minimal places where the braces
need to go, lateral and longitudinal, but you ned to do the work and then
prove it. Why then would you not include the calcs in your submittal?


On Thu, Feb 20, 2014 at 8:57 PM, Forest Wilson Fire Sprinkler Contractor <
[email protected]> wrote:

> Locate per 13 and send a calc sheet only if required in plan review.
>
>
>
> Forest Wilson
> Fire Sprinkler Contractor
> 937-736-0425
>
> Notice:
> This message is confidential. It may also be privileged or otherwise
> protected by work product immunity or other legal rules. If you have
> received it by mistake, please let us know by e-mail reply and delete it
> from your system; you may not copy this message or disclose its contents to
> anyone. Please send us by fax any message containing deadlines as incoming
> e-mails are not screened for response deadlines. The integrity and security
> of this message cannot be guaranteed on the Internet.
>
> -------- Original message --------
> From: "rongreenman ." <[email protected]>
> Date:02/20/2014  11:36 AM  (GMT-05:00)
> To: [email protected]
> Subject: Re: seismic bracing calcs
>
> From the Piemontesi to the greasy Sicilian, with molte amore. I won't hold
> it against you that your family is from the rock of hell in the Med 'cause
> you always explain the problem so clearly. And Letyon's OK too.
>
>
> On Thu, Feb 20, 2014 at 8:09 AM, Steve Leyton <[email protected]
> >wrote:
>
> > Right - all of the above.   We put the calc's on our detail sheet(s)
> > next to enlarged sketches of the proposed anchorage.
> >
> > Steve L.
> >
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > Brian Harris
> > Sent: Thursday, February 20, 2014 6:32 AM
> > To: [email protected]
> > Subject: RE: seismic bracing calcs
> >
> > Both...
> >
> > Brian Harris, CET
> > BVS Systems Inc.
> > bvssytemsinc.com
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > [email protected]
> > Sent: Thursday, February 20, 2014 9:27 AM
> > To: [email protected]
> > Subject: seismic bracing calcs
> >
> > Seismic design category C, contractor submittal package,
> >
> > Do you provide a calc sheet for EQ bracing or just locate per NFPA 13
> > and send typical catalog data sheets?
> >
> > FM Global project, BTW.
> >
> > Craig L. Prahl, CET
> > Fire Protection Group Lead
> > CH2MHILL
> > Lockwood Greene
> > 1500 International Drive
> > Spartanburg, SC  29303
> > Direct - 864.599.4102
> > Fax - 864.599.8439
> > CH2MHILL Extension  74102
> > [email protected]
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to