Thanks Duane.   I didn't have the standard with me and asked the client
if he'd looked at Chapter 3, which he said he had.   I would have gone
there myself if I wasn't so lazy ...

Steve 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Johnson, Duane (NIH/OD/ORS) [C]
Sent: Friday, February 21, 2014 3:52 AM
To: [email protected]
Subject: RE: Bathroom/powder room/toilet room

3.3.2 Bathroom.   Within a dwelling unit, any room or compartment
dedicated to personal hygiene, containing a toilet, sink, or bathing
capability such as a shower or tub.

A.3.3.2 Bathroom.   A room is still considered a bathroom if it contains
just a toilet. Additionally, two bathrooms can be adjacent to each other
and are considered separate rooms, provided they are enclosed with the
required level of construction. A compartment containing only a toilet,
regardless of its intended use, is considered a bathroom.

An interesting note...the existing hotel/dorm chapter 29 of NFPA 101
(2013) has an exception for not installing sprinklers in bathrooms...
29.3.5.5    In guest rooms and in guest room suites, sprinkler
installations shall not be required in closets not exceeding 24 ft2 (2.2
m2) and in bathrooms not exceeding 55 ft2 (5.1 m2).

However, this exception does not exist for new hotel/dorms chapter 28 of
NFPA 101. Interpret this as you may. Also, NFPA 101 (the code),
supersedes NFPA 13 (the standard).


Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Steve Leyton [mailto:[email protected]]
Sent: Thursday, February 20, 2014 7:40 PM
To: [email protected]
Subject: Bathroom/powder room/toilet room

2013 edition of 13 now requires sprinklers in all bathrooms except
conforming small ones in hotels.   Anyone have insight on whether the
toilet-only compartment of a larger bathroom is considered a "bathroom"
or could that be excepted.  How about a powder room that has no cabinets
or tub/shower but does have a basin and a toilet?

 

Steve Leyton

PROTECTION DESIGN & CONSULTING

2851 Camino del Rio South, Suite 400

San Diego, CA 92108

-------------------------------------------------------------

Ph:      858.751.2930 - ext. 102

Fax:    858.751.2933

Cell:  619.972.5696

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to