Same thing happened in Denver when all the jaws hit the ground.

On Fri, Feb 21, 2014 at 1:33 PM, Steve Leyton <[email protected]>wrote:

> That's what you think.   Go here:
> http://aki.bc.edu/cgi-bin/NESN/recent_events.pl
>
> Most recent temblors in New England were last week.  Not big ones, but
> you have them all the time.   This feeds into what I said about changing
> times: those maps in the annexes of older NFPA 13 editions are obsolete.
> Throw them away.
>
> There was also a pretty severe jolt on Jan 18 that was thought to be a
> seismic event but turned out to be about 1.3 million people all sitting
> down at the same time when the clock ran out on the Pats in the AFC
> Championship game.
>
> Steve
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> Todd - Work
> Sent: Friday, February 21, 2014 1:21 PM
> To: [email protected]
> Subject: Re: seismic bracing calcs
>
> I think you also need to take into account regional differences. Some
> areas, like Leytonland, have a lot of earthquakes and potential for
> serious ones in the future. They need to be on top of that. The last
> major earthquake in New England was in 1755 off the coast of MA.
> Earthquake potential is not taken as seriously out here. You go to
> places like TX and it is virtually non-existant. There isn't the
> consistent demand on a national level.
>
> The only time in the last 10 years I have had a direct involvement with
> a structural engineer in when one guy used all his mechanical dead loads
> to support the solar panels and forgot about the 3 - 8" mains directly
> underneath going to the ESFR systems (which somehow was my fault). The
> mechanical engineer looks to see if we meet their spec, the architect
> wants to make sure it looks pretty, the insurance company reviews it for
> their requirements and the AHJ does his check list. That is the reality
> of the review process. Structural guys are nowhere to be found. If they
> want a higher level of analysis, it is going to have to come from the
> design team. The sprinkler community is not going to start it.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
>
> > On Feb 21, 2014, at 1:18 PM, <[email protected]> wrote:
> >
> > I think the reason we are so far behind other trades is that for years
> and years fire sprinklers were considered a necessary evil and not an
> integral part of the building system. And in years past building
> structures weren't engineered to save every ounce of steel so supporting
> the added weight of a sprinkler system was no big deal.
> > Ron F
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > Steve Leyton
> > Sent: Friday, February 21, 2014 10:27 AM
> > To: [email protected]
> > Subject: RE: seismic bracing calcs
> >
> > This goes to perpetuate the notion that we're different or special and
> > that's good and okay.   I respectfully disagree - it's not.
> >
> > Every other discipline is required to structurally engineer their
> supports, coordinate loads and attachments closely with the structural
> engineer, show calculations for all of that and seismic support where
> required.  Why are we different - because we haven't been doing that the
> last 30 years while all the other building systems have moved forward to
> what are now the widely considered good practices for attaching building
> systems to structure?  Sorry, but if that's true then we're a bunch of
> retards who are allergic to change and that's a decidedly bad thing.
> >
> > I cannot tell you how many seismic braces I've seen attached to the
> bottom of composite I-joists.  Not the bottom of the web, the flat
> bottom of the bottom chord.  Or to the web of an 8" 20-gauge Z-purlin.
> > Or to an unreinforced metal deck.   Is that okay because, "We've
> always
> > done it like that?"   I've seen 4" main trapezed between two 16"
> > I-joists with a 2x4 - everyone cool with that?    Never mind the 2x4,
> we
> > know that's not cool but can those joists handle it?  Why do we think
> that the manufacturers of engineered wood structural products all now
> > publish sprinkler hanger and bracing handbooks?   BECAUSE THESE ARE
> > ENGINEERED SOLUTIONS, that's why.   So if you don't have a
> > pre-engineered solution you have to design one, i.e. coordinate your
> attachment points, calculate your seismic braces, verify with structural
> > that the building can handle the loads you're applying.   We are
> > currently working on a storage facility with poor water pressure and
> the structural engineer redesigned the roof structure to support the
> several dozen feet of 8" we've been forced to use to avoid a pump.  No
> big deal, just had to show him our design.
> >
> > To not take it to this degree of detail, i.e. to coordinate your work
> > with the affected work of other disciplines (structural) in the year
> > 2014 is not an adequate degree of diligence, IMHO
> >
> > <CRACK!!>   Oops, my soapbox just broke.
> >
> > Steve Leyton
> >
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > John Denhardt
> > Sent: Friday, February 21, 2014 9:12 AM
> > To: '[email protected]'
> > Subject: RE: seismic bracing calcs
> >
> > Agree 100%!
> >
> > John August Denhardt, P.E., FSFPE
> > Strickland Fire Protection Incorporated
> > 5113 Berwyn Road
> > College Park, Maryland 20740
> > Office Telephone Number:  301-474-1136 Mobile Telephone Number:
> > 301-343-1457 FIRE SPRINKLERS SAVE LIVES - Can you live without them?
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> > Steven Scandaliato
> > Sent: Thursday, February 20, 2014 5:13 PM
> > To: [email protected]
> > Subject: Re: seismic bracing calcs
> >
> > Well that's were we are going to disagree...I haven't put tick marks
> on a dwg or required them on a dwg since I can't remember. if a licensed
> contractor who employs certified (licensed in some states) fitters who
> cannot read a tables that tells him where to put a hanger based a pipe
> size then we got way bigger problems than seismic features...
> >
> > Sent from my BlackBerry 10 smartphone.
> > From: [email protected]
> > Sent: Thursday, February 20, 2014 4:04 PM
> > To: [email protected]
> > Reply To: [email protected]
> > Subject: RE: seismic bracing calcs
> >
> >
> > It's a miracle if they remember to show hangers on drawings and
> they're actually legible.
> >
> >
> >
> >
> > Craig L. Prahl, CET
> > Fire Protection Group Lead
> > CH2MHILL
> > Lockwood Greene
> > 1500 International Drive
> > Spartanburg, SC  29303
> > Direct - 864.599.4102
> > Fax - 864.599.8439
> > CH2MHILL Extension  74102
> > [email protected]
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of
> rongreenman .
> > Sent: Thursday, February 20, 2014 4:33 PM
> > To: [email protected]
> > Subject: Re: seismic bracing calcs
> >
> > You ought to be demanding it in that detail, Craig.
> >
> >
> >> On Thu, Feb 20, 2014 at 11:36 AM, <[email protected]> wrote:
> >>
> >> Steven,
> >>
> >> I have never received a contractor shop drawing that covered things
> >> to
> >
> >> the detail you describe.  It's often a wonder to get the basic
> >> information on the drawings like pipe elevations and hangers let
> >> alone
> >
> >> anything to the depth you describe.
> >>
> >> I don't disagree with your statement just saying, I've never seen it
> >> happen.
> >>
> >> Craig L. Prahl, CET
> >> Fire Protection Group Lead
> >> CH2MHILL
> >> Lockwood Greene
> >> 1500 International Drive
> >> Spartanburg, SC  29303
> >> Direct - 864.599.4102
> >> Fax - 864.599.8439
> >> CH2MHILL Extension  74102
> >> [email protected]
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected] [mailto:
> >> [email protected]] On Behalf Of Steven
> >> Scandaliato
> >> Sent: Thursday, February 20, 2014 11:00 AM
> >> To: [email protected]
> >> Subject: RE: seismic bracing calcs
> >>
> >> Wait...hold on...just to make sure, and Craig I am sure you probably
> >> know this...BUT we have a lot more than just calcs for braces that
> >> have to be addressed.  We have 4 other design features that have to
> >> be
> > addressed.
> >> Cplgs, clearance, separation and restraint.  This is a weakest link
> >> kinda thing...so just because we have braced a system does not mean
> >> it
> >
> >> is designed for seismic...we have to put flex and rigid cplgs where
> >> they go, we have to show that we have accounted for clearance where
> >> it
> >
> >> applies, we have to acknowledge that there is no separation required
> >> if applicable and we have to show and space b'line restraint.
> >> Seismic
> >
> >> design demands its own sheets and symbols and sheet installation
> >> notes
> >
> >> etc.  Do not try and pile all of this onto an already unreadable
> >> piping plan.  EOR or Shop design, all of these categories must be
> >> addressed in the documents....and by the way, putting 4-ways and
> >> every
> >
> >> change of direction is not a design feature required or intended by
> >> 9.3.  I see a lot of contractors do that thinking they are in
> >> compliance.  This may be a great cost saver or standardized thing you
>
> >> want to do with your fitters but it does not automatically put you in
> > compliance with 9.3....just sayin.
> >>
> >> One other note while I am on this, we all need to pay better
> >> attention
> >
> >> to restraint.  I still have many AHJs and contractors alike that
> >> haven't heard of it.  If seismic is required then restraint is
> >> required.  This isn't optional.  And pay attention to the spacing
> >> requirements for it.  Many, including myself, have fallen into the
> >> "end of line" mentality and think that is the only place we have to
> >> have it...but if you have long branchlines, you definitely will have
> > more than "end of line" locations.
> >>
> >> With Sicilian Love,
> >>
> >> Steven Scandaliato, SET CFPS
> >> 520.971.2322 Cell
> >> Skype: steven.scandaliato
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of
> >> rongreenman .
> >> Sent: Thursday, February 20, 2014 9:41 AM
> >> To: [email protected]
> >> Subject: Re: seismic bracing calcs
> >>
> >> Cliff's opinion is right.
> >>
> >>
> >> On Thu, Feb 20, 2014 at 6:49 AM, Cliff Whitfield
> >> <[email protected]>wrote:
> >>
> >>> Craig,
> >>>
> >>> If you don't calc it, how do you know it works?  That would be like
> >>> sending in drawings with 'hydraulically calculated pipe sizes' with
> >>> no hydraulic calcs to prove the sizes are correct.  Just not
> > happening.
> >>>
> >>> A lot of 'East Coast' contractors/designers (I fit in that category
> >>> even though I now live in Colorado) just show braces on their
> >>> drawings but it's not even close to being the correct way to do it.
> >>> They need to take the time to learn from the AFSA classes that Ken
> >>> Wagonner and others do so that they can do it right.  I've had to
> >>> take it 3 times because I don't use it very often and it easy to
> >>> forget without the repetition but it's just something you have to do
> >
> >>> if you are doing your
> >> job correctly.
> >>>
> >>> Simply my opinion (but I think it's right!)
> >>>
> >>> Cliff Whitfield, SET
> >>> President
> >>> Fire Design, Inc.
> >>> Ph: 719-488-3479
> >>>
> >>>
> >>>
> >>> [email protected]
> >>> www.fire-design.com
> >>>
> >>> -----Original Message-----
> >>> From: [email protected]
> >>> [mailto:[email protected]] On Behalf Of
> >
> >>> [email protected]
> >>> Sent: Thursday, February 20, 2014 7:27 AM
> >>> To: [email protected]
> >>> Subject: seismic bracing calcs
> >>>
> >>> Seismic design category C, contractor submittal package,
> >>>
> >>> Do you provide a calc sheet for EQ bracing or just locate per NFPA
> >>> 13 and send typical catalog data sheets?
> >>>
> >>> FM Global project, BTW.
> >>>
> >>> Craig L. Prahl, CET
> >>> Fire Protection Group Lead
> >>> CH2MHILL
> >>> Lockwood Greene
> >>> 1500 International Drive
> >>> Spartanburg, SC  29303
> >>> Direct - 864.599.4102
> >>> Fax - 864.599.8439
> >>> CH2MHILL Extension  74102
> >>> [email protected]
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kl
> >>> er.org
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kl
> >>> er.org
> >>
> >>
> >>
> >> --
> >> Ron Greenman
> >> Instructor
> >> Fire Protection Engineering Technology Bates Technical College
> >> 1101 So. Yakima Ave.
> >> Tacoma, WA 98405
> >>
> >> [email protected]
> >>
> >> http://www.bates.ctc.edu/fireprotection/
> >>
> >> 253.680.7346
> >> 253.576.9700 (cell)
> >>
> >> Member:
> >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >>
> >> They are happy men whose natures sort with their vocations. -Francis
> >> Bacon, essayist, philosopher, and statesman (1561-1626)
> >>
> >> A problem well stated is a problem half solved. -Charles F.
> >> Kettering,
> >
> >> inventor and engineer (1876-1958)
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
> >> l
> >> er.org
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
> >> l er.org _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
> >> l
> >> er.org
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> > Bacon, essayist, philosopher, and statesman (1561-1626)
> >
> > A problem well stated is a problem half solved. -Charles F. Kettering,
>
> > inventor and engineer (1876-1958)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er
> > .org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)