We have an AHJ requiring a 50 psi test on CPVC piping, we think that is 
excessive, and have always used 20 psi max. I know the best practice is to do a 
hydrostatic test, but thanks to the polar vortex we are having freezing 
temperatures and the builder needs to close up his walls. Right now we are 
looking for chapter and verse as to what the maximum recommended pressure is 
for an air test. Have looked through 3 different CPVC installation handbooks 
but the number is not jumping out at me. The TYCO Residential Dry System runs 
10 - 15 psi pressure. Note: This is not  a residential dry system we are trying 
to air test a system so the drywall can go on. When the building gets the heat 
turned on it will be a wet system.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to