The inspector wants to see an air test we give him an air test within reason. 
23° at job site were not putting water in the system under any condition.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Tuesday, February 25, 2014 1:32 PM
To: [email protected]
Subject: RE: Air Testing CPVC Piping

I fail to see the connection between closing walls and doing a hydro test or 
substitute air test.  Closing the walls is about is the pipe installed, hangars 
right, size right..... Yep it's all there, close it up and test later.  Nothing 
I know of that requires exposed testing. 

If it leaks as an inspector I don't care if your floors or walls get wet.  I 
only care the gauge stays at 200 psi for two hours.  As an inspector I don't 
care if it's hard to find said leaks after covering up.  When the gauge says 
200 for two hours you get you approval.  At what point in the project is 
irrelevant. Even in a dry system we air test (because we have to) and that one 
week in July when it's above freezing here we go back and hydro the systems.

Now as a contractor I surely would love to test everything before things are 
closed up but sometimes you just can't.    

Chris Cahill, PE*
Associate Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Richard 
Mote
Sent: Tuesday, February 25, 2014 11:46 AM
To: [email protected]
Subject: Air Testing CPVC Piping

We have an AHJ requiring a 50 psi test on CPVC piping, we think that is 
excessive, and have always used 20 psi max. I know the best practice is to do a 
hydrostatic test, but thanks to the polar vortex we are having freezing 
temperatures and the builder needs to close up his walls. Right now we are 
looking for chapter and verse as to what the maximum recommended pressure is 
for an air test. Have looked through 3 different CPVC installation handbooks 
but the number is not jumping out at me. The TYCO Residential Dry System runs 
10 - 15 psi pressure. Note: This is not  a residential dry system we are trying 
to air test a system so the drywall can go on. When the building gets the heat 
turned on it will be a wet system.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to