Todd,

Will the heads under the ducts cover the areas where you need them without
the sidewalls?  If the duct is so low that the sidewalls spray into the side
of it, seems like the heads under duct would be out of the way of the
sidewall spray and should work fine.

Send me a drawing if you want to.  You've got my email.  Not that my opinion
carries much weight but I can give it to you anyway :)

Cheers,

Cliff Whitfield, SET
President
Fire Design, Inc.
Ph: 719-488-3479
 
 

[email protected]
www.fire-design.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd -
Work
Sent: Tuesday, February 25, 2014 2:33 PM
To: [email protected]
Subject: Re: Coverage for obstructed sidewalls

Can't lower them because we would then be too far down

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Feb 25, 2014, at 4:11 PM, "G. Tim Stone" <[email protected]> wrote:
> 
> Todd, Can the Sidewalls be lowered? Or is the duct to deep?
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
> 
>                117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                           [email protected]
> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd
> -
>> Work
>> Sent: Tuesday, February 25, 2014 1:45 PM
>> To: [email protected]
>> Subject: Coverage for obstructed sidewalls
>> 
>> I have a situation where some sidewalls sprinklers are obstructed by
>> ductwork. Would it be acceptable to install additional pendents under the
>> ductwork to alleviate the issue?
>> 
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> www.fpdc.com
>> 860-535-2080 (ofc)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to