Steve-
I thought about that but it seems to apply to the bottom chord of the truss and 
not the 3/4" (in this case) diagonal braces.....

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Wednesday, February 26, 2014 4:16 PM
To: [email protected]
Subject: RE: Bar Joist Webs & EC HEADS

Use the "4 x C or D whichever is greater" figure from Section 8.8.


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian 
Harris
Sent: Wednesday, February 26, 2014 1:08 PM
To: [email protected]
Subject: Bar Joist Webs & EC HEADS

8.4.3 (2007) Says that EC heads can be installed "within" trusses as long as 
the web members do not exceed 1", is there anything that says how close to a 
web they can be?

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>