As George was fond of saying (I believe the original quote was by Roland). "ESFR is not a sprinkler system it's a building system" that may not be the exact quote but it's close.
Richard L. Mote Rowe Sprinkler Systems, Inc. 7994 Route 522, Suite 1 PO Box 407 Middleburg, PA 17842 P 570-837-7647 F 570-837-6335 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Tony Silva Sent: Thursday, February 27, 2014 1:23 PM To: [email protected] Subject: Re: ESFR sprinklers Thanks, Brad & Ron. I thought moving the heater may be the only answer. Though how you can do that with a 10'x10' ESFR spacing beats me. Tony ----- Original Message ----- From: [email protected] To: [email protected] Sent: Thursday, February 27, 2014 6:55:11 AM Subject: RE: ESFR sprinklers There is really no reason to use 165's, we use only 212's. I'm not aware of any 286F ESFR's but I haven't really look for them either. AFSA has great sprinkler head chart on their web site. And George was right, usually the unit heaters have to be moved because of the spacing limitations of ESFR's. It takes a lot of coordination early on in the project to prevent obstructions. We have the best results when we're on board before the structural design is completed. Ron F -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Tony Silva Sent: Wednesday, February 26, 2014 11:51 PM To: [email protected] Subject: ESFR sprinklers Using k=25.2 ESFR sprinklers at the ceiling in a storage application calculating 12 heads as per NFPA 13, (1) Can the heads be 165 deg.F or must they be 212 deg.F? (assuming no heat sources) (2) If there is a heat source, such as a unit heater, are there ESFR heads rated for 286 deg.F? I see only 165 & 212. Thanks, Tony _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org