Noted your inputs.My assumptions are as follows
with k16.8,20 spks and at 50psi remotest pressure works for 2733gpm with
15% addition of hydraulic imbalance.
adding 500gpm as hose allowance the total demand is 2733+500=3233gpm.

Lets assume the pressure side,
the remotest spk pr. is 50psi+line loss 50psi+static loss of44'(19.16psi)
upto BOR-bottom of riser.

having noted that the pump house is fed by 8" pipe length of 900ft. which
is the governing factor to match the requirement of pump discharge head.

based on the above info, the pr. reqd at BOR is 120psi with a flow of
3250gpm approx. the selection of the pump should be 3500gpm, with 18" pipe
of 900ft requires a pump discharge pressure as 145psi,since to reduce the
pressure loss in 900ft length to 20psi.
Adding booster pump will not be required,instead change your main pump to
3500gpm at 145psi.
If you can send me the layout of the sprinkler drawing and the fire pump
location(setting out plan), i can recheck and confirm once again to meet
the actual requirement needed for the system.


regards
DR
ae.linkedin.com/pub/radhakrishnan-duraikkannu/38/a05/285/



Regards


D RADHAKRISHNAN

MANAGER - Engineering & Estimation
SAMAY MIDDLE EAST TRADING LLC
PO BOX: 128089, Al Quoz Industrial Area-2,Dubai,UAE
Tel: 00971 4 3381 200(2 Lines), Fax: 00971 4 3381 300
Mobile: 050-1643785, email : [email protected], [email protected],
[email protected],Web site: www.samayprojects.in



On Tue, Mar 18, 2014 at 8:50 PM, Gerzayn Fuentes @ CEPI.MX <
[email protected]> wrote:

> Good morning to all of you.
> I have a project for a roll paper storage in a warehouse with 44' height.
> The FM Global design is 20 K16.8 @ 50 psi + 500 gpm by 120 minutes.
> The fire pump is 2,500 gpm @ 125 psi and the water tank for 269,924 gals.
> The preliminary calculations give me 2,130 gals @ 145 psi at the BOR.
> The pump room and tank is about 900 ft. from the BOR and have 8" PVP pipe.
> The grid system is: 8" primary main, 4" secondary main, 2.5" branch lines.
> The sprinkler head are pendent connected through arm-over of 1.5" pipe.
>
> The issue here is that the distance and Pipe size from the BOR and
> Pump give a lot of pressure and velocity.
>
> What do you recommend to work around?
> Booster pump near the BOR?
>
> Regards!
>
> ________________________________
> This year we are focused on improving our service ... Your feedback is
> extremely helpful. Feel free to support us.
> Have a safe day!
>
> Ing Gerzayn Fuentes Campos | Director
> CEPI Specialist in Fire Projects.
> Tel +52 (81) 1766-0800 x 106 | http://www.cepi.mx
>
> Regia Vista # 500  | Linda Vista |  Guadalupe  | Nuevo Leon |  Mexico  |
> 67130
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to