better yet a 2,500 gpm pump.

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Mar 19, 2014, at 5:17 AM, [email protected] wrote:

> 
> Also based on your flow requirements of 3233, a 3000 gpm pump would be more 
> than sufficient owing to the fact that the pump can run up the curve to 4500 
> gpm.