Perhaps I should have been clearer on the application. This is a OH II warehouse with bar joist construction and the lights suspended down from the deck at an elevation beneath the sprinkler deflectors. I thought that I could either apply the exception 8.6.5.2.1.4 or stay at least 24in away from the lights with my sprinklers and be code compliant. Have I been wrong all these years?
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jeremy Frazier Sent: Monday, March 24, 2014 1:04 PM To: [email protected] Subject: RE: NFPA 13 (07ed) 8.6.5.1 Well if its light hazard I would point out to him that 8.6.5.2.2 would be the applicable rule (if they are suspended from the ceiling), other than that, the only other rules you can use are table 8.6.5.1.2 or 8.6.5.1.2 (2) -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Martinez, Dewayne Sent: Monday, March 24, 2014 11:36 AM To: SprinklerFORUM Subject: NFPA 13 (07ed) 8.6.5.1 I have an AHJ telling me that a sprinkler must comply with both sections of 8.6.5.1. The problem I am having is the he is telling me that the suspended lights must comply with the table 8.6.5.1.2 (beam rule) because it is part of 8.6.5.1 even though the edge of the lights are at least 24in away from the sprinkler. The beam rule would require them to be at least 3ft away to comply. Any good idea how to respond to this? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org