A.8.6.5.2.1.4 It is the intent of this section to exempt nonstructural elements 
in light and ordinary hazard occupancies from the obstruction criteria commonly 
called the "Three Times Rule." However, the other obstruction rules, including 
the "Beam Rule" (8.6.5.1.2) and the "Wide Obstruction Rule" (8.6.5.3.3), still 
apply. If an obstruction is so close to a sprinkler that water cannot spray on 
both sides, it is effectively a continuous obstruction as far as the sprinkler 
is concerned and the Beam Rule should be applied.

It is not the intent of this section to permit the use of fixtures and 
architectural features or treatments to conceal, obscure, or otherwise obstruct 
sprinkler discharge. The requirement should be applied in accordance with the 
performance objectives in 8.6.5.1.


Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Martinez, Dewayne [mailto:[email protected]] 
Sent: Monday, March 24, 2014 2:26 PM
To: [email protected]
Subject: RE: NFPA 13 (07ed) 8.6.5.1

Perhaps I should have been clearer on the application.  This is a OH II 
warehouse with bar joist construction and the lights suspended down from the 
deck at an elevation beneath the sprinkler deflectors.  I thought that I could 
either apply the exception 8.6.5.2.1.4 or stay at least 24in away from the 
lights with my sprinklers and be code compliant.
Have I been wrong all these years?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jeremy 
Frazier
Sent: Monday, March 24, 2014 1:04 PM
To: [email protected]
Subject: RE: NFPA 13 (07ed) 8.6.5.1

Well if its light hazard I would point out to him that 8.6.5.2.2 would be the 
applicable rule (if they are suspended from the ceiling), other than that, the 
only other rules you can use are table 8.6.5.1.2 or
8.6.5.1.2 (2) 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Martinez, 
Dewayne
Sent: Monday, March 24, 2014 11:36 AM
To: SprinklerFORUM
Subject: NFPA 13 (07ed) 8.6.5.1

I have an AHJ telling me that a sprinkler must comply with both sections of 
8.6.5.1.  The problem I am having is the he is telling me that the suspended 
lights must comply with the table 8.6.5.1.2 (beam rule) because it is part of 
8.6.5.1 even though the edge of the lights are at least 24in away from the 
sprinkler.  The beam rule would require them to be at least 3ft away to comply. 
 Any good idea how to respond to this?

Thanks,

Dewayne 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to