Rod,

I experienced this exact situation.  In order to blow it in the drywall has
to be in place on the underside with installation holes bored in the decking
above.  The holes (typically 2") have to be properly placed and spaced and
are left open after installation for inspection where a stick is used to
determine if there are any voids.  Where a void exists the stick will cause
the insulation level to drop requiring it to be topped off. It's a ton of
work to avoid putting sprinklers in a qualified concealed space.

PS, If they ever ever open the ceiling, oh boy, like an hour glass it pours
out requiring reinstallation of semi rigid insulation such as roxul or
thermafiber.

I have pics if you want to see, off list.


John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank
Red Bank, New Jersey
Email: [email protected]
Cell/Text: 732-904-6823


 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Monday, March 24, 2014 4:59 PM
To: [email protected]
Subject: truss filled with insulation



I have an apartment building where the architect took the area increases for
a full 13 system. They are utilizing a 16"open web truss in between the
floors. The mechanical is running hvac in the truss. The sections show the
space filled with insulation with an accompanying note that states that it
will be. My question is how is this "completely filled with non -
combustible insulation?" They are planning on blowing in the insulation
around all the duct etc that is in the space but it just seems really hard
to believe that it will indeed be completely filled. I remember a while back
Roland tried to get a 2" gap on the top and I think that was a battle. I am
picturing the duct blocking insulation from getting in plenty of spots.
Maybe not? Any thougts?

Rod at Rapid
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to