Thanks Bob,

I kept digging, found this verbiage in 1999 NFPA 13, 7-4.1.5.3  Located in the 
Rack Storage Section. It was also applicable for areas that are highly 
susceptible to water damage.

"Where preaction systems are used, preaction systems shall be treated as dry 
pipe systems.

Exception: This requirement shall not apply where it can be demonstrated that 
the detection 
system that activates the preaction system causes water to be discharged from 
sprinklers as 
quickly as the discharge from a wet pipe system."

This was new for 1999.  So that answers two questions, this was not in force in 
1982 and what's there now doesn't have a snowball's chance of working 
correctly.  I can duplicate the original design if I calc it using C-120 for a 
wet system, if you use C-100 for black steel, dry system as it actually exists, 
the system is non-functional. 


NFPA 13, 2010 has removed this statement from all areas within where it used to 
reside.

Oh the fun of it all.   

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bob
Sent: Monday, March 31, 2014 4:22 PM
To: [email protected]
Subject: RE: Single interlock PA equal to Wet

2002 ed, 12.2.3.2.2.5 (B)

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, March 31, 2014 2:03 PM
To: [email protected]
Subject: Single interlock PA equal to Wet

At some point in time I thought I had seen a blurb in NFPA 13 which stated that 
for some certain design conditions a single interlock preaction system was 
considered the same as a wet pipe system.  The rationale behind the premise 
being that the system piping would be charged prior to activation of 
sprinklers.  Trying to look for a similar statement in NFPA 13 2010, and not 
just finding it.  

Anyone recall this in prior or the 2010 edition?


Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to