A couple of years ago Michelin, the French tyre manufacturer, used a 3rd variant of PA in their unheated warehouses where freezing may happen: The system they used was a SIPA but if the detector failed and the sprinkler activated then the system acted as a dry pipe system.
May be they still use it.
The intend of the detection was to have water in the network and ready available near at the sprinklers faster then an ordinary dry system can.
The detection was by rate-of-rise detectors.

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112


At 17:35 31-3-2014 -0700, you wrote:
I've always seen a SIPA as a wet with empty piping until a smoke alarm, or
some other detection that's more sensitive than heat detection filling the
pipe in anticipation of a head fusing. Same with a DIPA except it's becomes
a DPV when that sensitive detection releases it to respond as a normal dry
pipe would if a head also fuses. since both are "pre-action" what is: 1,
the pre-action and 2, the action? Viking's definitions seem to suggest pre
means changing from a state similar to a closed control valve on either a
SIPA or DIPA into post pre state, becoming the equivalent of a wet or a dry
pipe respectively.

Supervisory air in a SIPA has nothing to do with activation, just
notification if the system integrity is compromised, and the higher
pressure air in a DIPA fulfills that function when the detection is holding
the valve in a pre state.

I think (that might be a problem) that the definition of pre-action and the
explanatory annex material  (2013) is wholly inadequate, and the commentary
in the handbook regarding DIPA sounds like it was written by a salesman
trying to promote the most complicated, and therefore, costly system. Apart
from the comment that accidental discharge is rare, it sounds like the only
way to alleviate such a fear is with DIPA, in my opinion (there's that
problem again) an inappropriate solution unless rapid freezing (two or
three hours or less, or getting a technician out would be longer and it's
so cold that a freeze-up would occur faster than that, say a freezer
warehouse, or a loading dock in Frozen Butte, Montana in winter) is
anticipated.

But the book says what it says and Roland will tell me to write a change
suggestion if I don't like it, and I'm speculating and not directly
addressing the topic, and Steve M. having to weigh in recently and probably
still a little sensitive, and of course opening myself to the possibility
of another salvo from Steve L. (although with admittedly the best filthy
epithet fired in my direction in recent memory), I shall bid you all adieu.


On Mon, Mar 31, 2014 at 4:43 PM, Brad Casterline <[email protected]>wrote:

> Picking up where your but... left off Ron I thought the same thing if you
> were thinking this is a matter of Definition trumps Operation. And we
> cannot plan for failure of the detection system any more than we can plan
> for the fire not starting in one place on the floor, but... half-way up a
> combustible wall in a room with a combustible ceiling.
>
> > On Mar 31, 2014, at 5:33 PM, "rongreenman ." <[email protected]>
> wrote:
> >
> > Seems odd as it should be filled with water before a single head fuses so
> > it should act like a wet, but if the detection fails to trip the valve no
> > number of heads opening will make it act like a dry. It would have
> > deterioration characteristics similar to dry sitting around with wet air
> in
> > it all day so the 100C would make sense, but....
> >
> >
> >> On Mon, Mar 31, 2014 at 1:59 PM, <[email protected]> wrote:
> >>
> >> Not in the 1979 edition of NFPA 231 which is what is applicable to my
> >> project for the original design.  So the exception was not present in
> the
> >> Storage standard in 1979 and didn't make it to NFPA 13 until 1999.  That
> >> makes it irrelevant for the original design.
> >>
> >> It is not applicable based on current NFPA 13 either, so it is what it
> is,
> >> a dry system by definition.
> >>
> >>
> >>
> >> Craig L. Prahl, CET
> >> Fire Protection Group Lead
> >> CH2MHILL
> >> Lockwood Greene
> >> 1500 International Drive
> >> Spartanburg, SC  29303
> >> Direct - 864.599.4102
> >> Fax - 864.599.8439
> >> CH2MHILL Extension  74102
> >> [email protected]
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected] [mailto:
> >> [email protected]] On Behalf Of
> rongreenman .
> >> Sent: Monday, March 31, 2014 4:41 PM
> >> To: [email protected]
> >> Subject: Re: Single interlock PA equal to Wet
> >>
> >> If it wasn't editions previous to 1999 could it have been in a 231
> series
> >> document since that's the year when 231 and 231C were folded into 13?
> >>
> >>
> >>> On Mon, Mar 31, 2014 at 1:32 PM, <[email protected]> wrote:
> >>>
> >>> Thanks Bob,
> >>>
> >>> I kept digging, found this verbiage in 1999 NFPA 13, 7-4.1.5.3
> >>> Located in the Rack Storage Section. It was also applicable for areas
> >>> that are highly susceptible to water damage.
> >>>
> >>> "Where preaction systems are used, preaction systems shall be treated
> >>> as dry pipe systems.
> >>>
> >>> Exception: This requirement shall not apply where it can be
> >>> demonstrated that the detection system that activates the preaction
> >>> system causes water to be discharged from sprinklers as quickly as the
> >>> discharge from a wet pipe system."
> >>>
> >>> This was new for 1999.  So that answers two questions, this was not in
> >>> force in 1982 and what's there now doesn't have a snowball's chance of
> >>> working correctly.  I can duplicate the original design if I calc it
> >>> using
> >>> C-120 for a wet system, if you use C-100 for black steel, dry system
> >>> as it actually exists, the system is non-functional.
> >>>
> >>>
> >>> NFPA 13, 2010 has removed this statement from all areas within where
> >>> it used to reside.
> >>>
> >>> Oh the fun of it all.
> >>>
> >>> Craig L. Prahl, CET
> >>> Fire Protection Group Lead
> >>> CH2MHILL
> >>> Lockwood Greene
> >>> 1500 International Drive
> >>> Spartanburg, SC  29303
> >>> Direct - 864.599.4102
> >>> Fax - 864.599.8439
> >>> CH2MHILL Extension  74102
> >>> [email protected]
> >>>
> >>>
> >>>
> >>> -----Original Message-----
> >>> From: [email protected] [mailto:
> >>> [email protected]] On Behalf Of Bob
> >>> Sent: Monday, March 31, 2014 4:22 PM
> >>> To: [email protected]
> >>> Subject: RE: Single interlock PA equal to Wet
> >>>
> >>> 2002 ed, 12.2.3.2.2.5 (B)
> >>>
> >>> Thank You,
> >>>
> >>> Bob Knight, CET III
> >>> 208-318-3057
> >>> www.Firebyknight.com
> >>>
> >>>
> >>> -----Original Message-----
> >>> From: [email protected]
> >>> [mailto:[email protected]] On Behalf Of
> >>> [email protected]
> >>> Sent: Monday, March 31, 2014 2:03 PM
> >>> To: [email protected]
> >>> Subject: Single interlock PA equal to Wet
> >>>
> >>> At some point in time I thought I had seen a blurb in NFPA 13 which
> >>> stated that for some certain design conditions a single interlock
> >>> preaction system was considered the same as a wet pipe system.  The
> >>> rationale behind the premise being that the system piping would be
> >>> charged prior to activation of sprinklers.  Trying to look for a
> >>> similar statement in NFPA 13 2010, and not just finding it.
> >>>
> >>> Anyone recall this in prior or the 2010 edition?
> >>>
> >>>
> >>> Craig L. Prahl, CET
> >>> Fire Protection Group Lead
> >>> CH2MHILL
> >>> Lockwood Greene
> >>> 1500 International Drive
> >>> Spartanburg, SC  29303
> >>> Direct - 864.599.4102
> >>> Fax - 864.599.8439
> >>> CH2MHILL Extension  74102
> >>> [email protected]
> >>>
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >>> er.org
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >>> er.org _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >>> er.org
> >>>
> >>
> >>
> >>
> >> --
> >> Ron Greenman
> >> Instructor
> >> Fire Protection Engineering Technology
> >> Bates Technical College
> >> 1101 So. Yakima Ave.
> >> Tacoma, WA 98405
> >>
> >> [email protected]
> >>
> >> http://www.bates.ctc.edu/fireprotection/
> >>
> >> 253.680.7346
> >> 253.576.9700 (cell)
> >>
> >> Member:
> >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >>
> >> They are happy men whose natures sort with their vocations. -Francis
> >> Bacon, essayist, philosopher, and statesman (1561-1626)
> >>
> >> A problem well stated is a problem half solved. -Charles F. Kettering,
> >> inventor and engineer (1876-1958)
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>
> >
> >
> >
> > --
> > Ron Greenman
> > Instructor
> > Fire Protection Engineering Technology
> > Bates Technical College
> > 1101 So. Yakima Ave.
> > Tacoma, WA 98405
> >
> > [email protected]
> >
> > http://www.bates.ctc.edu/fireprotection/
> >
> > 253.680.7346
> > 253.576.9700 (cell)
> >
> > Member:
> > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> > They are happy men whose natures sort with their vocations. -Francis
> Bacon,
> > essayist, philosopher, and statesman (1561-1626)
> >
> > A problem well stated is a problem half solved. -Charles F. Kettering,
> > inventor and engineer (1876-1958)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to