standard spray or sidewall or residential pendent or ???? Obstructed or
unobstructed construction??
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
On 4/14/2014 4:42 PM, [email protected] wrote:
What is the maximum allowable distance a sprinkler head can be below a
ceiling. I believe it is 12". Can anybody confirm?
Thanks
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org