That may be a factor Mike, I didn't know that.

But twice we let the system settle for several hours and it would finally 
settle at 80-75 psi.

I would like it to be just a expansion but don't think so.

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407

> On Apr 15, 2014, at 5:03 PM, Mike Cabral <[email protected]> wrote:
> 
> The PE pipe will expand and you will see a pressure drop as a result. Take a 
> look at some of the PEX mfg sites and you will find data regarding testing 
> methods. 
> 
> Sent from my iPhone
> 
>> On Apr 15, 2014, at 8:39 AM, Aaron Peck <[email protected]> wrote:
>> 
>> No, I got that.
>> 
>> The plumber is telling me that it's not a leak in the underground but in the 
>> lead-in connections for individual office containers. Got 20 individual 
>> containers outfitted for office and living quarters. There's aboveground PE 
>> pipe and where they connect he says that's the area of leaks. Dropping about 
>> 50 psi from 200 psi over 5 mins.
>> 
>> Trying to figure out how many gpm need to leak for a 50 psi drop.
>> 
>> Sent from my iPhone
>> Aaron M. Peck, SET Fire Protection
>> Skype +1(202)407-9079
>> Cambodia +855(0)78700407
>> 
>>> On Apr 15, 2014, at 3:42 PM, [email protected] wrote:
>>> 
>>> Are you talking about the allowable loss for underground systems?
>>> 
>>> Craig L. Prahl, CET   
>>> Fire Protection Group Lead
>>> CH2MHILL
>>> Lockwood Greene
>>> 1500 International Drive
>>> Spartanburg, SC  29303
>>> Direct - 864.599.4102
>>> Fax - 864.599.8439
>>> CH2MHILL Extension  74102
>>> [email protected]
>>> 
>>> 
>>> 
>>> -----Original Message-----
>>> From: [email protected] 
>>> [mailto:[email protected]] On Behalf Of Aaron 
>>> Peck
>>> Sent: Tuesday, April 15, 2014 3:54 AM
>>> To: [email protected]
>>> Subject: Finding a formula
>>> 
>>> I can't seem to find one but I'm trying to find the volume of water loss 
>>> during a pressure test. I can get the total volume of water in the pipe but 
>>> can't seem to find a formula to help with finding the volume loss.
>>> 
>>> Sent from my iPhone
>>> Aaron M. Peck, SET Fire Protection
>>> Skype +1(202)407-9079
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to