The 20 PSI limit is actually based on the federal Clean Water Act and some 
states have also adopted as law or regulation. I know NJ has it as regulation. 

Dave Herbert
Retired from NJ
Fire guy in the Sunshine State
Guest

Sent from my iPhone

> On May 14, 2014, at 9:53, "Mark A. Sornsin, P.E." <[email protected]> 
> wrote:
> 
> Craig, it has been my understanding that the 20psi number represents the 
> lowest residual pressure fire departments 'generally' want to see when 
> drawing from a municipal supply - to avoid the potential for collapsing mains 
> at some higher elevation than where the water is being drawn. There are 
> exceptions such as in flat areas like Fargo where they can safely drop below 
> 20 psi in most circumstances. So the flow at 20psi generally represents the 
> maximum flow rate they can safely achieve at that point on the system.
> 
> It is a 'fictional' number since in most cases they are using extrapolation 
> to get to it.  On the other hand, it's not all that fictional if your test 
> from which the extrapolation is run produced a 25% pressure drop from the 
> static.  That drop helps define an accurate 'slope' on the N^1.85 graph. 
> Determining the flow at 20 psi does not warrant multiple significant digits - 
> certainly fewer than in sprinkler design (which should use a couple at most). 
> The extrapolation won't be that far off from reality.
> 
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer 
> | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: [email protected] [mailto:[email protected]]
> Sent: Wednesday, May 14, 2014 8:42 AM
> To: Mark A. Sornsin, P.E.; [email protected]
> Subject: RE: Can a hydrant flow from the pumper connection be used for the 
> hydraulic calculations ?
> 
> And there's another point of discussion, how about that extrapolation at 20 
> psi.
> 
> What is the value of that number in reality?
> 
> I've seen 20 psi flow rates that we knew without any doubt were unachievable 
> by the municipal water supply yet when trying to convince an owner that the 
> water supply would not meet his system demand and the site would require a 
> pump and tank, they would quickly point to the 20 psi flow rate and say 
> "there, see we've got lots of water!"   It just confuses the uninformed.
> 
> I've also seen the additional data point of how much flow you get when at 0 
> psi.  I'm still trying to get my head around that one.  Maybe someone can 
> explain it.
> 
> So why put these fictional numbers on a test report?
> 
> 
> 
> Craig L. Prahl, CET
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Mark A. Sornsin, P.E.
> Sent: Wednesday, May 14, 2014 9:34 AM
> To: [email protected]
> Subject: RE: Can a hydrant flow from the pumper connection be used for the 
> hydraulic calculations ?
> 
> Steve - you seem to be off on a tangent and did not understand the question. 
> Its o.k. - that happens at your age.
> 
> I agree with Travis. I have done several water flow tests using the 4-1/2" 
> port.  Apply the proper coefficients and life is good. Of course, flowing 
> that port can have logistical problems due to the large amount of water 
> and/or damage cause by the discharge - so be careful, plan accordingly, or 
> find an alternative approach if necessary.
> 
> But he raises another peeve of mine. Further to Ron's comments, why do we 
> have to reduce residual pressure to the point of being at least 25% lower 
> than the static? If my sprinkler design anticipates 700 gpm for sprinklers 
> and hose combines, and I run a flow test that produces 1,000 gpm with only a 
> 1 psi drop in pressure, why would I attempt to open more ports or hydrants?
> 
> In this example we have a flat curve. We're going to need to flow a huge 
> amount of water relative to my design demand to achieve the prescribed 25% 
> drop. To what benefit would we do such a thing? The only reason I can imagine 
> is "because our contract/AHJ says so" - which a crappy reason, but may be 
> legit, sadly.
> 
> My personal belief is that 291 requires a certain drop in pressure because 
> they want better accuracy for when they extrapolate to a residual pressure of 
> 20 psi.  I.e., the flow test is for fire departments to evaluate available 
> firefighting water for their purposes - not necessarily for sprinkler design 
> purposes.  Will this method give more accurate result for sprinkler design as 
> well? Yes - but too often it is a level of accuracy not needed (as in my 
> example above) and is not worth the effort expended.
> 
> 
> 
> Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer 
> | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
> http://www.kfiengineers.com
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Travis Mack
> Sent: Tuesday, May 13, 2014 4:12 PM
> To: [email protected]
> Subject: Re: Can a hydrant flow from the pumper connection be used for the 
> hydraulic calculations ?
> 
> Are you asking if you can do a flow test from the pumper connection?  If so, 
> then sure you can.  You just need to modify the coefficient based on your 
> pitot.
> 
> How are you inflating the gpm?  If you measure 1200 gpm from the 2½" and you 
> measure 2000 gpm from the 4.5", how is that inflating flow?  You should 
> typically have a lower residual pressure when flowing the pumper connection 
> than the 2½" connection.
> 
> If you are looking to 291 for direction, are you getting the required 25% 
> drop in static and residual from your 2½" flow?  If not, what do you do?  You 
> are required to open up additional hydrants to get the flow.
> So, to get additional flow, you can also flow from the pumper connection.
> 
> Maybe I am misunderstanding your question.
> 
> Travis Mack, SET
> MFP Design, LLC
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> For more information please visit http://www.symanteccloud.com 
> ______________________________________________________________________
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to