Adding to Craig,  it depends on the codes and standards they follow (or don't), 
 NFPA-70-Article 695, 700 and NFPA-20 are clear on the arrangement.

John

John Drucker, CET
Assistant Construction Official
Fire Protection Subcode Official
Building/Fire/Electrical Inspector
Borough of Red Bank, New Jersey
Office: 732-530-2760 X 331
Cell/Text: 732-904-6823
Email: [email protected]
http://www.redbanknj.org



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Friday, May 16, 2014 8:05 AM
To: [email protected]; [email protected]
Subject: RE: Electric Fire Pump Normal Power Source

When dealing with foreign installations, your code requirements may be 
meaningless.

Is there an enforced building/fire code?

Is the owner directed by or operates under the recommendations of an Insurance 
Underwriter?

Basically, unless there is an enforced building code, you may be just wasting 
your time.

Craig L. Prahl, CET   
Fire Protection Group Lead
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Aaron Peck
Sent: Friday, May 16, 2014 2:15 AM
To: [email protected]
Subject: Electric Fire Pump Normal Power Source

Ok guys I'm not familiar enough with power source requirements so looking for 
guidance.

I have a client trying to some how get out of buying the Fire Pump with a 
transfer switch.

This is located in Cambodia so it's not looking good. It's in the capital but 
because I live here so I know they haven't got a year without a power outage 
lasting more than 4 hours. Plus they have a on-site generator.

So we have 2 sources of power and they have their own transfer switch. They 
want to pull a dedicated line from their transfer switch.

I think this violates section 9.2.3, I'm not sure but I think there are more 
than 1 disconnect upstream. Unless it could be a feeder connection by 9.2.2(4).

And per 9.3.1 we don't even have a FDC because the fire department won't do 
anything even if it is burning.

So I see a connection from the main electrical coming in and another main line 
from the generator itself. Not from their transfer switch.

Am I right in my thinking?

Sent from my iPhone
Aaron M. Peck, SET Fire Protection
Skype +1(202)407-9079
Cambodia +855(0)78700407
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to