it isn’t the type of structure but the applied standard that dictates the 
requirements for an FDC.  Note that 13R has an exception for small buildings 
less than 2,000 sf.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On May 22, 2014, at 9:54 AM, [email protected] wrote:

> 
> Hello
> 
> this has to do with when egress windows are not provided in 1-2 family 
> dwellings, and the sprinkler has to be designed per 13R as per IBC
> is there an exception or industry std on whether to provide a local flow 
> alarm and fire dept connection
> 13 R says they are required 
> does a private home need a fdc and a bell
> 