Reza,

What Ron said is good. I would also say that if you use NFPA standards, you 
will get a system that works. A lot of what is in them has come from research 
or forensic analysis so there is a track record. Stick with a design based on 
NFPA 13, 14, 20, 22, 24 and whatever else is appropriate. Keep in mind, these 
are standards, not codes.

Best of luck.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On May 28, 2014, at 10:17 PM, "rongreenman ." <[email protected]> wrote:
> 
> Reza,
> 
> You don't need an alarm check valve (ACV). A riser consists of a single
> control valve, a check valve, a gauge on the system side of the check valve
> (and preferably another on the supply side), a main drain, a means to alarm
> (flow switch), and a means to initiate the alarm. An ACV juste incorporates
> all these in one device.
> 
> You should have a check valve, a control valve and a mean to drain the
> floor. You should also have a flow alarm on each floor.
> 
> The fire pump needs a jockey and a skid with pump, jockey, and controllers
> is likely to be better and more reliable than a field built set-up.
> 
> Sleeping rooms of hotels are always light hazard, as are assembly/meeting
> areas, with service areas being OH1.
> 
> Water tank, if you're only concerned with the sprinklers, is the density
> times the design area plus inside hose stream times the duration. Example:
> (0.1 gpm x 1500 sqft + 150 gpm) x 30 min = 9000 gallons. If your potential
> discharge rate is greater then I'd multiply that plus the hose stream times
> thirty. If you need to consider standpipe requirements then that needs to
> be added.
> 
> I'm sure you'll get differing opinions of minimum but under the
> circumstances you describe, especially considering the lack of regulation,
> the available dollars, and the likely quality of installation expertise in
> Iraq....
> 
> 
> On Wed, May 28, 2014 at 7:13 AM, Reza Esmaeili 
> <[email protected]>wrote:
> 
>> Dears All,
>> I know this question may be very cheap, but there is no codes in my
>> country and I have to design a cost effective sprinkler system which just
>> works, I don't need to comply any codes. By the way, I am living in Iraq,
>> I would like to know the most cost-effective sprinkler system that can be
>> designed for a 6 stories hotel/office building which needs about 60
>> sprinkler heads.
>> - is it accessory to instal a wet alarm valve? Can i delete wet alarm
>> valve and use a control valve with flow switch at each floor?
>> - Can i use only a single electric driven fire pump instead of an
>> expensive complex booster pump set?
>> - What is the minimum water tank size I should consider?
>> 
>> Note: The buildings don't have parking lot, so I consider it as a light
>> hazard occupancy (0.1 GPM/ft2 over 1500 ft2).
>> 
>> 
>> Thanks & Regards,
>> Reza
>> Etalon Security
>> Erbil / Iraq
>> +964 750 961 5318
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to