Reza, What Ron said is good. I would also say that if you use NFPA standards, you will get a system that works. A lot of what is in them has come from research or forensic analysis so there is a track record. Stick with a design based on NFPA 13, 14, 20, 22, 24 and whatever else is appropriate. Keep in mind, these are standards, not codes.
Best of luck. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc) > On May 28, 2014, at 10:17 PM, "rongreenman ." <[email protected]> wrote: > > Reza, > > You don't need an alarm check valve (ACV). A riser consists of a single > control valve, a check valve, a gauge on the system side of the check valve > (and preferably another on the supply side), a main drain, a means to alarm > (flow switch), and a means to initiate the alarm. An ACV juste incorporates > all these in one device. > > You should have a check valve, a control valve and a mean to drain the > floor. You should also have a flow alarm on each floor. > > The fire pump needs a jockey and a skid with pump, jockey, and controllers > is likely to be better and more reliable than a field built set-up. > > Sleeping rooms of hotels are always light hazard, as are assembly/meeting > areas, with service areas being OH1. > > Water tank, if you're only concerned with the sprinklers, is the density > times the design area plus inside hose stream times the duration. Example: > (0.1 gpm x 1500 sqft + 150 gpm) x 30 min = 9000 gallons. If your potential > discharge rate is greater then I'd multiply that plus the hose stream times > thirty. If you need to consider standpipe requirements then that needs to > be added. > > I'm sure you'll get differing opinions of minimum but under the > circumstances you describe, especially considering the lack of regulation, > the available dollars, and the likely quality of installation expertise in > Iraq.... > > > On Wed, May 28, 2014 at 7:13 AM, Reza Esmaeili > <[email protected]>wrote: > >> Dears All, >> I know this question may be very cheap, but there is no codes in my >> country and I have to design a cost effective sprinkler system which just >> works, I don't need to comply any codes. By the way, I am living in Iraq, >> I would like to know the most cost-effective sprinkler system that can be >> designed for a 6 stories hotel/office building which needs about 60 >> sprinkler heads. >> - is it accessory to instal a wet alarm valve? Can i delete wet alarm >> valve and use a control valve with flow switch at each floor? >> - Can i use only a single electric driven fire pump instead of an >> expensive complex booster pump set? >> - What is the minimum water tank size I should consider? >> >> Note: The buildings don't have parking lot, so I consider it as a light >> hazard occupancy (0.1 GPM/ft2 over 1500 ft2). >> >> >> Thanks & Regards, >> Reza >> Etalon Security >> Erbil / Iraq >> +964 750 961 5318 >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > > > -- > Ron Greenman > Instructor > Fire Protection Engineering Technology > Bates Technical College > 1101 So. Yakima Ave. > Tacoma, WA 98405 > > [email protected] > > http://www.bates.ctc.edu/fireprotection/ > > 253.680.7346 > 253.576.9700 (cell) > > Member: > ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC > > They are happy men whose natures sort with their vocations. -Francis Bacon, > essayist, philosopher, and statesman (1561-1626) > > A problem well stated is a problem half solved. -Charles F. Kettering, > inventor and engineer (1876-1958) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org