You are not required to include them.  From the 2013 ed.

23.4.4.6.3 The requirements of 23.4.4.6.1.1 to include every
sprinkler in the design area shall not apply where spray sprinklers
or CMSA sprinklers are provided above and below obstructions
such as wide ducts or tables.

B.J. Newlin
Service Sales
Aegis Fire Protection LLC.

"Whoever is careless with the truth in small matters cannot be trusted with
important matters" 
― Albert Einstein




-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Jamie Seidl
Sent: Friday, June 06, 2014 7:37 AM
To: [email protected]
Subject: Sprinklers under duct

I seem to be drawing a blank and also can not find it in the standard, so if
someone can tell me off the top of their head, I'd appreciate it.
Are standard spray sprinklers located under obstructions greater than 4'
required to be included in calculations?  I seem to remember, no they are
not, however the reference in the standard is eluding me.

Thanks,
Jamie Seidl