If there is an insurance company involved, you may want to check with them. I have had to include them in the past due to their requirements.
Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT www.fpdc.com 860-535-2080 (ofc) > On Jun 6, 2014, at 8:41 AM, "B.J. Newlin" <[email protected]> wrote: > > You are not required to include them. From the 2013 ed. > > 23.4.4.6.3 The requirements of 23.4.4.6.1.1 to include every > sprinkler in the design area shall not apply where spray sprinklers > or CMSA sprinklers are provided above and below obstructions > such as wide ducts or tables. > > B.J. Newlin > Service Sales > Aegis Fire Protection LLC. > > "Whoever is careless with the truth in small matters cannot be trusted with > important matters" > ― Albert Einstein > > > > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] > On Behalf Of Jamie Seidl > Sent: Friday, June 06, 2014 7:37 AM > To: [email protected] > Subject: Sprinklers under duct > > I seem to be drawing a blank and also can not find it in the standard, so if > someone can tell me off the top of their head, I'd appreciate it. > Are standard spray sprinklers located under obstructions greater than 4' > required to be included in calculations? I seem to remember, no they are > not, however the reference in the standard is eluding me. > > Thanks, > Jamie Seidl > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org