This most likely is from the International Fire Code, Chapter 5, Fire Service Features, (G) Section 507 Fire Protection Water Supplies. Subsection 507.3 says "fire flow requirements for building or portions of building and facilities shall be determined by an approved method". In Ohio, this has been adopted direct into the Ohio Administrative Code. I'm guessing any other jurisdiction using ICC are (or will) be doing the same.
Typically the local Fire Marshal will help facilitate the evaluation (to be conducted by a private fire protection/water utility contractor) and will be the one to review/approve it. Andrew Steele Dayton, OH (937) 333-4522 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Tim Stone Sent: Thursday, June 26, 2014 10:34 AM To: [email protected] Subject: Water Supply Has anyone in other parts of the country run across this? I just received a copy of a state fire marshal's review letter on a new project in which they are asking that the (Water supply for firefighting shall be evaluated and provided in accordance with NFPA 1142). Who is responsible for this evaluation in your area? Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 Fax: (802) 434-4343 <mailto:[email protected]> [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler .org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org