This most likely is from the International Fire Code, Chapter 5, Fire
Service Features, (G) Section 507 Fire Protection Water Supplies.
Subsection 507.3 says "fire flow requirements for building or portions
of building and facilities shall be determined by an approved method".
In Ohio, this has been adopted direct into the Ohio Administrative Code.
I'm guessing any other jurisdiction using ICC are (or will) be doing the
same.    

Typically the local Fire Marshal will help facilitate the evaluation (to
be conducted by a private fire protection/water utility contractor) and
will be the one to review/approve it. 

Andrew Steele
Dayton, OH
(937) 333-4522



-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of Tim
Stone
Sent: Thursday, June 26, 2014 10:34 AM
To: [email protected]
Subject: Water Supply

 

Has anyone in other parts of the country run across this?

I just received a copy of a state fire marshal's review letter on a new
project in which they are asking that the (Water supply for firefighting
shall be evaluated and provided in accordance with NFPA 1142).

 

Who is responsible for this evaluation in your area?

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

                117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343

                            <mailto:[email protected]>
[email protected]

                                

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to