Just wondering how an architect can be an EOR.  An architect is not an engineer.

Sent from my iPhone

> On Jun 26, 2014, at 10:25 AM, "Tim Stone" <[email protected]> wrote:
> 
> Craig,
> 
> In this case I was hired by the Architect to design a Sprinkler system for a
> brand new Church. The project is in a rural setting so fire pump and tanks
> are being used. Is it reasonable for the AHJ to expect the NICET certified
> designer to perform this duty or shouldn't this responsibility fall back
> onto the Architect who in this case would be the EOR?
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
> 
>                 117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                            [email protected]
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of [email protected]
> Sent: Thursday, June 26, 2014 11:03 AM
> To: [email protected]
> Subject: RE: Water Supply Evaluation
> 
> Is your project a rural or suburban project?
> 
> Fire flow requirements should be identified by the EOR with direction from
> the local or otherwise applicable fire authority.
> 
> I typically make a call to the local fire authority to find out what method
> is used to determine fire flow.  There are several different methods out
> there with requirements that vary greatly so guessing isn't a wise move.
> 
> Once we know their approved method, we apply that info and determine what is
> required to meet Code.  Sometimes that entails a tank and pump, sometimes
> not.  
> 
> Fire Flow is one thing that gets overlooked a lot in engineering design.  We
> recently had one contractor telling an owner that the requirements for fire
> flow were ridiculous and he's never had to do that anywhere else.  I hope he
> doesn't do much design beyond 7-11 stores with his level of knowledge of the
> Codes.
> 
> Craig L. Prahl 
> Fire Protection Group Lead
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29303
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of Steele, Andrew
> Sent: Thursday, June 26, 2014 10:47 AM
> To: [email protected]
> Subject: RE: Water Supply Evaluation
> 
> This most likely is from the International Fire Code, Chapter 5, Fire
> Service Features, (G) Section 507 Fire Protection Water Supplies.
> Subsection 507.3 says "fire flow requirements for building or portions of
> building and facilities shall be determined by an approved method".
> In Ohio, this has been adopted direct into the Ohio Administrative Code.
> I'm guessing any other jurisdiction using ICC are (or will) be doing the
> same.    
> 
> Typically the local Fire Marshal will help facilitate the evaluation (to be
> conducted by a private fire protection/water utility contractor) and will be
> the one to review/approve it. 
> 
> Andrew Steele
> Dayton, OH
> (937) 333-4522
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of Tim
> Stone
> Sent: Thursday, June 26, 2014 10:34 AM
> To: [email protected]
> Subject: Water Supply
> 
> 
> 
> Has anyone in other parts of the country run across this?
> 
> I just received a copy of a state fire marshal's review letter on a new
> project in which they are asking that the (Water supply for firefighting
> shall be evaluated and provided in accordance with NFPA 1142).
> 
> 
> 
> Who is responsible for this evaluation in your area?
> 
> 
> 
> Regards,
> 
> G. Tim Stone
> 
> 
> 
> G. Tim Stone Consulting, LLC
> 
> NICET Level III Engineering Technician
> 
> Fire Protection Sprinkler Design
> 
> and Consulting Services
> 
> 
> 
>                117 Old Stage Rd. - Essex Jct., VT. 05452
> 
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
> 
>                            <mailto:[email protected]>
> [email protected]
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to