When you run these numbers what value do you use for the flow in the line at 
the static pressure reading, our do you assume a hydrant on a dead end main 
with zero flow for an actual static pressure reading?
Mark at Aero

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Thursday, June 26, 2014 9:58 AM
To: [email protected]
Subject: RE: Underground Piping

Makes sense Todd.

I believe a flow test measures the friction loss from the source to the gauged 
hydrant, with a negligible amount of velocity head loss. Say we get 75,72,500. 
If we know 8" X 1500 feet total, using Q^1.85 and rearranging H-W, we can get 
the C-Factor=140. If we got 75,68,500 with the same 8 by 1500, we would get 
C=85. Also, using Q^2 and C=140, we would get the same 7 pound drop. I guess 
what I am saying is, the flow test is a measure of the several factors, as a 
whole, that are usually unknown without doing a lot of digging, literally ;)

Brad   


-----Original Message-----
From: Todd - Work [mailto:[email protected]]
Sent: Thursday, June 26, 2014 10:18 AM
To: [email protected]
Subject: Re: Underground Piping

Remember, all of our formulas are approximations. They can be more accurate in 
some situations and less in others. The velocity restrictions of years back 
were originally to compensate for the inaccuracies in the formula when velocity 
exceeded a certain amount.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to