Dear all,
Thanks for all the comments, here I answer some of the questions:
- There is no necessity to follow any cods in Iraq, there is no national code 
for fire.
- The AHJ is Fire Department, they don't have any knowledge about fire 
sprinklers and they let us design as we wish.
- There is no central monitoring.
- I suppose that in case of fire, it takes about 15 minutes for fire 
departments to come.

Regards,
Reza 
Etalon Security,
Erbil - Iraq

------------------------------
On Thu, Jun 26, 2014 7:11 PM IRDT Travis Mack wrote:

>Reza:
>
>A few questions:
>
>Do you have central monitoring? If so, this cuts your duration down to 30 min 
>for light hazard. So, if you have QR sprinklers and can reduce to 900 sq ft, 
>then you have 90 gpm for 30 min in light hazard. That is only 2700 gallons. 
>
>Do you have any kind of municipal supply at all. Let's say you have a demand 
>of 0.2 over 1500 for 60 min (ord grp 2). If the city can deliver 250 gpm, you 
>can use a break tank to make up the 50 gpm shortage. This would be a 3000 
>gallon tank with a 60 min duration. 
>
>Do you have a good response time from the fire service? If so, maybe you can 
>negotiate a shorter water supply duration. Let's say you need 300 gpm for 60 
>min per NFPA 13. If you have a quick FD response, you may be able to negotiate 
>a 10 min water supply. 
>
>I'm not sure if any of this will help. I'm just trying to think outside of the 
>box for you.
>
>PS: praying you stay safe, my friend. 
>
>Travis Mack, SET
>MFP Design, LLC
>
>Sent from my iPhone
>
>> On Jun 26, 2014, at 6:58 AM, Matt Grise <[email protected]> wrote:
>> 
>> Reza,
>> 
>> In most areas of the US it is realistic to assume that the public water 
>> supply will deliver enough water for both the sprinklers and hoses for the 
>> fire fighters.
>> 
>> Regarding your question about how much water is enough water... The codes 
>> suggest a minimum amount that can be reliably counted on to suppress a fire. 
>> If you do not have the space, structural capacity, or water available, then 
>> it is just not an option.
>> 
>> Of course, some is better than none. 
>> 
>> However - it would be a good idea to not rely too much on a system that 
>> could fail. There are many other ways to make a building safer beside fire 
>> sprinklers. If the sprinklers are not 100% reliable it would be a good idea 
>> to consider shorter exit paths, more exits, fire rated egress routes, fire 
>> resistant construction (finishes and structure), and other architectural 
>> options to increase occupant safety.
>> 
>> Not every car can be an armored tank... eventually you just have to do the 
>> best you can with what you have. If the building is going to be built I 
>> would say "follow all codes". If there is no way that is going to happen, I 
>> would say "make it as safe as you can".
>> 
>> **for the record - I definitely recommend following all codes all the time!
>> 
>> Matt Grisé PE*, LEED AP, NICET II  
>> Sales Engineer 
>> Alliance Fire Protection 
>> 130 w 9th Ave.
>> North Kansas City, MO 64116
>> 
>> *Licensed in KS & MO 
>> 
>> 913.888.0647 ph 
>> 913.888.0618 f 
>> 913.927.0222 cell 
>> www. AFPsprink.com 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:[email protected]] 
>> On Behalf Of Reza Esmaeili
>> Sent: Thursday, June 26, 2014 8:34 AM
>> To: [email protected]
>> Subject: Water Tank is so Big!
>> 
>> Hello All,
>> I would like to divide my question in three parts:
>> 
>> - What is the volume and pressure of public water supply in the US? I wonder 
>> why you don't usually feel any problem with the big amount of water required 
>> for sprinklers and standpipe systems as per NFPA-13. Do you count on your 
>> public water supply or you always consider a private water tank for your 
>> sprinkler and standpipe system?
>> 
>> - While a 12,000 gallon water tank seems very realistic to use for a office 
>> building considered as a light hazard occupancy with design density of 0.1 
>> gpm per sq ft over 1500 sq ft. But we don't have such a big space in our 
>> buildings in Iraq to place the water tank because we usually don't have 
>> parking in our buildings to also place the water tank. What should we do?
>> 
>> - While 88% percent of fires are controlled only by 1 or 2 sprinklers 
>> activation, so is it really necessary to consider around 12 operating 
>> sprinklers which will make the water tank so big? I know you will say: "Yes, 
>> 88% is not 100%" but I say, we don't have such a big space, so most of the 
>> buildings will not install sprinklers at all. I say if I install a 3000 
>> gallon water tank which I have the space, it can supply enough water to at 
>> least 3 sprinklers and this will control 88% of fires and it is better than 
>> not installing sprinklers. Please suggest a realistic solution. 
>> 
>> Please don't suggest quick response sprinklers to reduce the size of design 
>> area, even with QR sprinklers, the water tank is so big!
>> 
>> Thanks,
>> Reza
>> www.etalonsecurity.com
>> Erbil / Iraq
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to