The Cooler is a closed in room with a space above. You calculate all the
heads inside the cooler if less than 1500 SF. If the area outside the cooler
is fully sprinklered then you probably have performed calcs already. I'd ask
the AHJ to review NFPA 13.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Bob
Sent: Friday, June 27, 2014 1:12 PM
To: [email protected]
Subject: Cooler Calc

I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler and
submitted.  The AHJ is telling me that I need to calc additional sprinklers
at the ceiling to have a 1500 sf design area.  I don't think I need to do
this, I was looking at this as a separate fire area, and I don't see it
being much different than not adding heads below ducts or other large
obstructions.  Do I need to calc additional sprinklers at the ceiling for
this application?

Thank You,

Bob Knight, CET III
208-318-3057
www.Firebyknight.com