He tried to claim NFPA 13R (2010) 5.3

"5.3* Underground Pipe. Any type of pipe or tube acceptable under the
plumbing code for underground supply pipe shall be acceptable as
underground supply for the system when in- stalled between the point of
connection and the system riser."

I replied that this section of NFPA 13R simply allows the pipe between
supply and system riser to be anything allowed in the plumbing code instead
of having a dedicated chapter for underground as in NFPA 13. This does not,
however, have any effect on materials after the system riser.

I also sent him the section from Tyco's Installation manual that applies to
Underground installations.

He must not have liked my response because now he is simply stating that
CPVC is only allowed underground before the riser. His argument is that the
Tyco Manual mentions "underground service" and not "sprinkler system
piping".

Thanks,

Tony Liddic, CET
MRH Sprinkler Design LLC
356 Laurel Glen Dr.
Springboro, OH  45066
937-369-7926
http://mrhsprinklerdesign.com
[email protected]



On Fri, Jul 18, 2014 at 9:47 AM, <[email protected]> wrote:

> How would the pipe know which side of the riser it's on?
> Mark at Aero
>
> Sent from my iPhone
>
> > On Jul 18, 2014, at 6:18 AM, "Tony Liddic" <
> [email protected]> wrote:
> >
> > I have a client that does a lot of typical apartment building in various
> > jurisdictions. The buildings are 3 stories with breezeways 1/3 of the way
> > down the length of the building.
> >
> > They are 13R systems and the client has always used Blazemaster CPVC.
> They
> > run a main down the center of the 1st floor, drop below the breezeway
> > underground then back up in a wall on the other side. This has never been
> > an issue until now.
> >
> > An AHJ is stating that the CPVC is not approved for underground use on
> the
> > system side of the riser, only the supply side.
> >
> > Any thoughts?
> >
> > Thanks,
> >
> > Tony Liddic, CET
> > MRH Sprinkler Design LLC
> > 356 Laurel Glen Dr.
> > Springboro, OH  45066
> > 937-369-7926
> > http://mrhsprinklerdesign.com
> > [email protected]
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to