Steve gives good advice, but be prepared for the AHJ to not take his
personality and self-worth out of the equation. I had an informal
interpretation once that the AHJ rejected. Unusual, but not unheard of.
This case was a little special as Roland had penned the response, which had
followed my previous reasoning and arguments exactly, and the AHJ's
response was, and I quote from memory, satisfied it's accurate enough,
"Whoever wrote this obviously has no understanding of what NFPA 13 means."
When I asked him if he knew who the author was he said he didn't care, nor
did it matter, as whoever it was didn't know what he was talking about. So
then you just comply.


On Fri, Jul 18, 2014 at 10:15 AM, Steve Leyton <[email protected]>
wrote:

> Tony:
>
> Here's an idea of how to take MOST of the subjectivity and personalities
> out of the equation.   Sometimes, when we have a difference of opinion
> with an AHJ, they ask the person on the other side of the counter to
> substantiate their position with a code or standards citation.   And
> sometimes, we ask them to substantiate their rejection of a proposed
> design or product application the same way.   And sometimes, what
> happens after that is that one or the other party interprets the cited
> code or standard differently and doesn't accept the substantiation.
> That's what has happened here; you said, "Here  - look at this
> manufacturer's listing data" and the AHJ is saying, "I don't think it
> applies."   And you can't cite anything more to say they're right or
> wrong: you're in the intractable "your word or opinion vs. theirs"
> vortex.
>
> So take YOUR personality and opinion out of the equation.   I think
> anyone with even a small measure of experience and reasoning skills
> would understand that as far as the product goes, there's absolutely no
> difference in the applications of supply-side vs. system-side.   NFPA
> standards describe specific thrust restraint exceptions for fusion joint
> piping installed underground.   The listing data incorporates
> underground installation, very clearly.   There are a host of
> circumstantial references that add up to what we all agree is the
> de-facto acceptability of CPVC underground, but the AHJ isn't having it.
> So the way to get them off the schneid is to have them correspond with
> the manufacturer.
>
> You ask them to substantiate the objection, they say that it's their
> opinion.  You explain that you've corresponded with the manufacturer who
> assures you that it's acceptable and then you facilitate the AHJ
> corresponding directly with the manufacturer.   "This company obtained
> the listing and wrote the installation guide and they say it's okay, so
> here's the number of their tech services department."  Or you get a rep
> to call the AHJ or you obtain a letter from the manufacturer and show it
> to the AHJ, but in any case take yourself out of the loop and have the
> AHJ obtain the information directly from the horse's mouth.   If the AHJ
> wants to second-guess someone, it's going to be a lot more challenging
> to question the representative o the company that oversaw testing of the
> product and then wrote the standards.
>
> Steve L.
>
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Tony Liddic
> Sent: Friday, July 18, 2014 7:22 AM
> To: sprinklerforum
> Subject: Re: Blazemaster CPVC Underground
>
> This AHJ is stating that the term "Underground Fire Service" in the
> installation manual means that the CPVC can only be used underground
> between system riser and water supply, not under the breezeways.
>
> Thanks,
>
> Tony Liddic, CET
> MRH Sprinkler Design LLC
> 356 Laurel Glen Dr.
> Springboro, OH  45066
> 937-369-7926
> http://mrhsprinklerdesign.com
> [email protected]
>
>
>
> On Fri, Jul 18, 2014 at 10:17 AM, Triolo, Joe <[email protected]>
> wrote:
>
> >
> > http://www.harvel.com/sites/www.harvel.com/files/documents/Fire_Sprink
> > ler-Installation_Instructions-English.pdf
> >
> > Look at Pages 20 and 21
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of Stafford,
>
> > Susan
> > Sent: Friday, July 18, 2014 9:51 AM
> > To: [email protected]
> > Subject: RE: Blazemaster CPVC Underground
> >
> > http://www.harvelblazemaster.com/specifications/scope-application
> >
> > Sue Stafford, SET  /  Sprinkler Design Technician IV/Tyco
> > SimplexGrinnell
> > Tel: +1-972-587-5200  /  Direct: +1 972-587-5246
> > 1125 E Collins Blvd.  /  Richardson, TX 75081  /  USA
> > [email protected]  /  www.tycosimplexgrinnell.com
> >
> >
> >
> > This email (including any attachments) may contain information that is
>
> > private or business confidential. If you received this email in error,
>
> > please delete it from your system without copying it and notify sender
>
> > by reply email so that our records can be corrected.
> > Tyco's vision is Zero Harm to people and the environment. Please
> > consider the environment before printing this message.
> >
> > -----Original Message-----
> > From: Sprinklerforum [mailto:
> > [email protected]] On Behalf Of Tony
> > Liddic
> > Sent: Friday, July 18, 2014 8:18 AM
> > To: sprinklerforum
> > Subject: Blazemaster CPVC Underground
> >
> > I have a client that does a lot of typical apartment building in
> > various jurisdictions. The buildings are 3 stories with breezeways 1/3
>
> > of the way down the length of the building.
> >
> > They are 13R systems and the client has always used Blazemaster CPVC.
> > They run a main down the center of the 1st floor, drop below the
> > breezeway underground then back up in a wall on the other side. This
> > has never been an issue until now.
> >
> > An AHJ is stating that the CPVC is not approved for underground use on
>
> > the system side of the riser, only the supply side.
> >
> > Any thoughts?
> >
> > Thanks,
> >
> > Tony Liddic, CET
> > MRH Sprinkler Design LLC
> > 356 Laurel Glen Dr.
> > Springboro, OH  45066
> > 937-369-7926
> > http://mrhsprinklerdesign.com
> > [email protected]
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> > ________________________________
> >
> > This e-mail contains privileged and confidential information intended
> > for the use of the addressees named above. If you are not the intended
>
> > recipient of this e-mail, you are hereby notified that you must not
> > disseminate, copy or take any action in respect of any information
> > contained in it. If you have received this e-mail in error, please
> > notify the sender immediately by e-mail and immediately destroy this
> > e-mail and its attachments.
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > er.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)