The AHJ told me "I don't care what the codes say. Do it my way or no CofO." I 
am appealing to the State FM while arranging to change the pumps to 2000 gpm. 
We have a written notice from the GC to get our plans approved. The GC has 
tried to reason with the badge. That's when he was told they would accept a 
fire watch until the pumps are changed.

Ron fletcher Sent from my iPhone

> On Jul 19, 2014, at 5:57 AM, "Johnson, Duane (NIH/OD/ORS) [C]" 
> <[email protected]> wrote:
> 
> And A.4.8. 
> 
> Duane
> 
> ----- Original Message -----
> From: Johnson, Duane (NIH/OD/ORS) [C]
> Sent: Saturday, July 19, 2014 08:56 AM Eastern Standard Time
> To: '[email protected]' 
> <[email protected]>
> Subject: Re: Segue to AHJ's from CPVC Underground
> 
> See NFPA 20:4.8.1. 
> 
> Duane
> 
> ----- Original Message -----
> From: [email protected] [mailto:[email protected]]
> Sent: Saturday, July 19, 2014 08:42 AM Eastern Standard Time
> To: [email protected] 
> <[email protected]>
> Subject: Re: Segue to AHJ's from CPVC Underground
> 
> The project is a 700k sq ft type Vb construction. B105.2 calls out 8000 GPM 
> fire flow. The locally adopted reduction is 50%, so 8000 x50% =4000 GPM. They 
> are correct about the flow rate. They just don't understand that that is what 
> is required from the municipal water system to the site for manual fire 
> fighting. They believe that out sprinkler booster pumps need to produce 4000 
> GPM at their 100% design point, and feel that operating a fire pump in excess 
> odors design point of 100% is somehow bad. 
> Mark at Aero
> 
> Sent from my iPhone
> 
>> On Jul 19, 2014, at 5:32 AM, "Johnson, Duane (NIH/OD/ORS) [C]" 
>> <[email protected]> wrote:
>> 
>> The question still stands why 4000? 
>> 
>> Duane
>> 
>> ----- Original Message -----
>> From: [email protected] [mailto:[email protected]]
>> Sent: Saturday, July 19, 2014 08:15 AM Eastern Standard Time
>> To: [email protected] 
>> <[email protected]>
>> Subject: Re: Segue to AHJ's from CPVC Underground
>> 
>> The stance of the AHJ is that their unwritten policy is pumps can only be 
>> used at 100%. They also believe that 1500 gpm pumps will only produce 1500 
>> gpm, and we have to use 2 2000 gpm pumps to get 4000 gpm. They don't think 
>> pressure is even a factor.
>> 
>> Ron fletcher Sent from my iPhone
>> 
>>> On Jul 19, 2014, at 5:00 AM, "Johnson, Duane (NIH/OD/ORS) [C]" 
>>> <[email protected]> wrote:
>>> 
>>> There are so many things wrong here. But, you may be able to make this work 
>>> regardless. Did you take your 75% reduction in fire flow based on the fully 
>>> sprinklered exception in B105.2? If you are starting at 4000 gpm, the 
>>> required flow can be reduced to 1500 gpm if fully sprinklered. Doesn't that 
>>> work with your pumps?  
>>> 
>>> Duane
>>> 
>>> ----- Original Message -----
>>> From: Johnson, Duane (NIH/OD/ORS) [C]
>>> Sent: Saturday, July 19, 2014 07:51 AM Eastern Standard Time
>>> To: '[email protected]' 
>>> <[email protected]>
>>> Subject: Re: Segue to AHJ's from CPVC Underground
>>> 
>>> Has Annex B been adopted?  See 101.2.1? 
>>> 
>>> Duane
>>> 
>>> ----- Original Message -----
>>> From: [email protected] [mailto:[email protected]]
>>> Sent: Saturday, July 19, 2014 07:35 AM Eastern Standard Time
>>> To: [email protected] 
>>> <[email protected]>
>>> Subject: Re: Segue to AHJ's from CPVC Underground
>>> 
>>> Hi John,
>>> What Ron didn't say is that the AHJ is trying to connect chapter 5 of the 
>>> IFC and table B105.2 fire flow requirements to our sprinkler system pumps. 
>>> We conceded early on to furnish a redundant pump because it was specified 
>>> that way, but the FM is expecting the fire pumps to provide the 4000 GPM 
>>> from B105.2 at the sprinkler (ESFR) demand pressure (165 PSI) and do so at 
>>> the 100% design point of the fire pump. We submitted our design with two 
>>> 1500 GPM pumps piped in parallel along with calcs for the storage 
>>> sprinklers flowing at around 165 PSI at the pump discharge. The city water 
>>> system which supplies the project flow tested at 5700 GPM at 74 PSI from 
>>> two 4" hydrant butts. No one at the AHJ's office understands how to read a 
>>> fire code, or any other code for that matter. They are "Code Alchemist", 
>>> taking a paragraph from chapter 5,  table from the annex, and numbers from 
>>> our calcs, mix 'em all together in an AHJ beaker and BOOM!! "Minimum code 
>>> requirement". See? This stuff a
 i
> n
>> 't
>>> all that hard.
>>> 
>>> Mark at Aero
>>> 602 820-7894
>>> 
>>> Sent from my iPad
>>> 
>>> On Jul 19, 2014, at 2:24 AM, "John Drucker" 
>>> <[email protected]<mailto:[email protected]>> wrote:
>>> 
>>> Like how you wrote; " everything is per code except we have".  "Except" ?, 
>>> Are you/they saying that having two pumps rather than one is a violation; 
>>> I.e. " 4000 GPM at 160 vs 4000 at 165" and you're short 5 psi ?  So two 
>>> code violations, two pumps and short 5 psi. Now before you chop my head 
>>> off, consider two things wheres the one pump and 165 psi coming from ? 
>>> Somehow apparently this has been planted in the ahjs head, I'm certain 
>>> he/she didn't come up with it on there own. Now you're stuck.  Frankly and 
>>> using common sense are you hitting demand, does everything fit and work 
>>> together, is the principal designer and owner ok with it ?  Move forward.
>>> 
>>> John Drucker - Mobile Email
>>> [email protected]<mailto:[email protected]><mailto:[email protected]>
>>> Cell/Text 732-904-6823
>>> 
>>> 
>>> [email protected]<mailto:[email protected]> wrote:
>>> 
>>> How about everything is per code except we have two pumps rather than 
>>> one.and we have 4000 GM at 160 psi instead of.4000 gpm at 165 psi. Most 
>>> ignorant thing I have ever seen. Just found out the chief told plan 
>>> reviewer no more written correspondence. I guess because they don't want a 
>>> written orecord of their stupidity. Please forgive my frustration but I 
>>> just don't know where to go from here..
>>> 
>>> Ron fletcher Sent from my iPhone
>>> 
>>> On Jul 18, 2014, at 4:24 PM, "John Drucker - Home" 
>>> <[email protected]<mailto:[email protected]>> wrote:
>>> 
>>> Ron, et.al.
>>> 
>>> I don't know the particulars of your situation but we have a saying; there's
>>> your side, their side and the truth.  Perhaps there's an issue with the code
>>> itself,  a local amendment or interpretation. There's got to be something
>>> driving this.
>>> 
>>> Case in point about a reference standard, NFPA-72 speaks of wall mounted
>>> smoke detectors/alarms and calls out a distance yet the illustration in the
>>> annex is worded differently than the code.
>>> 
>>> 29.8.3.3 Wall Mounting. Smoke alarms or smoke detectors mounted on walls
>>> shall be located NOT FARTHER than 12 in. (300 mm) from the adjoining ceiling
>>> surface.
>>> 
>>> Yet the annex A.29.8.3 notes;  "Measurements shown are to the closest edge
>>> of the detector".
>>> 
>>> According to the annex this would place part or most of the alarm or
>>> detector FARTHER than 12 in. from the adjoining ceiling surface.
>>> 
>>> It's important to note that Annex A opens with the following statement;
>>> 
>>> "Annex A is not a part of the requirements of this NFPA document but is
>>> included for informational purposes only. This annex contains explanatory
>>> material, numbered to correspond with the applicable text paragraphs"
>>> 
>>> Yet when brought to NFPA's attention the answer from the NFPA representative
>>> was interpreted from the Annex material.  This is clearly incorrect, the
>>> annex and the illustration are not part of the code.  In either case fix the
>>> code language or the annex.   The same happens in I Code Commentaries and
>>> various subject matter books that often interpret, amend or supplement the
>>> actual code language.  In a nutshell our codes and standards have become a
>>> maze of requirements, exceptions and interpretations.  This should be a
>>> warning flag to the code community.  Perhaps the code official has just
>>> reached his limit and is instead relying on empirical experience in the face
>>> of confusion.
>>> 
>>> I have situation at this very moment on two different projects that impose
>>> an operational issue for the fire department, one that the code is not
>>> considering.  However my approach is to get everyone around the table do
>>> some brainstorming and come up with an equitable technical solution.
>>> Perhaps by finding the root cause of your situation the stakeholders will
>>> put down their swords and solve the problem.   Food for thought.
>>> 
>>> Best wishes, always available should the need arise.
>>> 
>>> Sincerely,
>>> 
>>> John
>>> 
>>> John Drucker, CET
>>> Assistant Construction Official
>>> Fire Protection Subcode Official
>>> Building/Fire/Electrical Inspector
>>> Borough of Red Bank
>>> Red Bank, New Jersey
>>> Email: [email protected]<mailto:[email protected]>
>>> Cell/Text: 732-904-6823
>>> 
>>> Safe Buildings Save Lives !
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum [mailto:[email protected]]
>>> On Behalf Of [email protected]<mailto:[email protected]>
>>> Sent: Friday, July 18, 2014 1:04 PM
>>> To: 
>>> [email protected]<mailto:[email protected]>
>>> Subject: Segue to AHJ's from CPVC Underground
>>> 
>>> It's Friday so I figured I'd whine on the forum.  To set the stage, prior to
>>> the letter I am referring to we had approved permitted drawings from the
>>> AHJ. The following is a quote from a letter we received from that same AHJ.
>>> 
>>> "At this time , Blah Blah Blah Fire Protection District is denying said
>>> plans and is requesting a re-submittal of new plans that exceed IFC, UFC,
>>> and NFPA standards." Nowhere in the body of the letter does he say exactly
>>> how we are to "EXCEED" IFC, UFC and NFPA. In the letter they basically
>>> outline that what was submitted meets the all of the codes. I was told by
>>> the author of the letter at a meeting the day before that he didn't care
>>> what the code said because he is the AHJ and per Section 104 of the IFC he
>>> can make us do whatever he wants. Then he said "do it my way or there will
>>> be no Certificate of Occupancy."  We are 4-5 weeks away from a CofO and the
>>> change involves increasing the size of two new diesel pumps that are being
>>> installed. The fire chief told us to go to the State Fire Marshal if we
>>> wanted to appeal. I'm a bit frustrated with AHJ's right now.
>>> 
>>> Ron F
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]<mailto:[email protected]>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to